Generator Protections are:
1. over current protection
2. Earth Fault protection
3. under voltage protection
4. pole slipping protection
5. under frequency protection
6. Impedence protection
7. df/dt protection
Transformer Protections are:
1. Differential protection
2. winding temperature protection
3. Oil temperature protection
4. overcurrent protection
5. Earth fault protection
6. undercurrent protection
Note:
The protection relays are increases deponds on the ratings
of the Transformer and Generator...
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / parmod kumar
Generators Protection's are
1. over current protection
2. Earth Fault protection
3. under voltage protection
4. under frequency protection
5. Reverse Current Protection
6. High Water Temperature Protection
7. Low Coolent Water Level Protection
8. Over Speed Protection
9. Low Lub Oil Pressure Protection
Transformer Protections are
1. Winding Temprature Protection
2. Oil Temprature Protection
3. Bucholz relay protections
4. overcurrent protection
5. Earth fault protection
6. undercurrent protection
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / n k singh
Generator protection means protecting the generator in case
any abnormality occurs on generator and transformer
protection means protection of transformer in case any
abnormality occurs on transformer.
General generator protections are:
1.U/F Protection
2.U/V Protection
3.Excitation failure protection
4.Protection against prime mover failure.
General Transformer protections are:
1.Overload protection
2.Ground /Earth fault protection
3.Restricted earth fault protrection
4.Winding temperature high protection
5.Winding protection.
| Is This Answer Correct ? | 3 Yes | 2 No |
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
types of arc quenching methodes
Define step response?
how many current required for hypo test
i need project topics along with circuit diagram in the electrical and electronics engg and also some websites regarding projets.
why transformer rating comes in kva?
Is there thumb rule to calculate how many Insulators to be used for Transmission line of different volatges
Draw torque - speed curve and load curve of induction motor? mark operating point ?
why does same amount of current flow in the circuit inspite of any number of resistances in the circuit?
what is RR number Abbreviation energy meter
we have two 11/.433 kv. distribution Transformer rating as 1000 kva & 500 kva , i wants to run parallel both transformer. both transformer impendence voltage is 5.24%, How can we run both t/f, & how sharing the load
List the advantages of star-delta starter with induction motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)