how much current we can get from 11kv overhead line ?
Answers were Sorted based on User's Feedback
It is depends on the generating station MW capacity
| Is This Answer Correct ? | 19 Yes | 12 No |
Answer / prabhukumar
thats depends on the amount of load connected. depending on
that right material and protection will be used.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / a k kataria
Current to be drawn from 11kv line depends on different
factors.These factors are length of line, size of
conductor,ambient temperature of region etc.Normally 11 kv
line with Racoon conductor could carry 197 Amps and perhaps
with Dog conductor could carry 240 Amps with VD 6%.Also
Currents beyond this may create problems at breaker levls
as excessive heat coud result particularly at Joints.
| Is This Answer Correct ? | 8 Yes | 5 No |
Answer / mohamed
it is depend on the type of the conductor CU or Al
it is depend on the cross section area of the Conductor
R = resistevity * length / Area
1 MM^2 ----> Cu give between 3 --> 5 Amp.
1 MM^2 -----> Al give between 1 ---> 3 Amp
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / amit
it depends upon how much load is connected and generation side production capacity
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / dilip
it is depends on the rating of distribution transformer,e.g
if there is 100 kva, then it will take 5.25amp.
| Is This Answer Correct ? | 12 Yes | 14 No |
Answer / mahdi
this depend on headway , capacity of line , heavay of wagon
and dever of rail , capacity of traction motor ...
electrical_powerstation@yahoo.com
expert of OCS in mashhad iran
www.murco.ir
| Is This Answer Correct ? | 1 Yes | 8 No |
1.wat is the purpose (or)function of regulator? 2.wat is the purpose of stabiliser?
What is the Gap Should maintain for HT cables crossing of LT Cable?
The D.C. spark test is applicable to single conductor cable & assemblies of insulated single conductor cables without insulation shield,metallic sheath or metalic armor?
how to decide the capacity of accl
What will happen when more than one star neutral points at same voltage level are connected to earth by metallic conductor?
how to convert psi into kilo pascal? what is the suction pressure & discharge pressure of chiller?
i have been tasked with a design of protection, metering and control(PMC) relay panel extension to accommodate all PMC relays.There is an already existing panel where this one will be built.What are the design aspects for this kind of project? thank you.
flush point of transformer?
what is the difference between a frequecy converter and an electric inverter?
how dc load convert to ac load
In all electric motors, fans are provided to dissipate heat. How it dissipate the heat? By absorbing atmospheric air or by exhausting the heated air generated while running?
what is the size of ht cable of 33kv ht line and transformers ratings are 1 Mva and 5mva.please send formula also.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)