Necessity of transformer earthing
Answer / gunasekaran
for neutral earthing
1.for three four wire sys.
2.if it source end it should be earthed because earth fault
current getting return path.
3.resonance is avoided.
4.for distribution load to maintain the balance condition.
5.at earth fault condition ifit is solidly grounded voltage
buidup at another two phase are getting only 80%line voltage
so no insulation problem.
for body earthing
1. to avoid the shock.
| Is This Answer Correct ? | 8 Yes | 3 No |
What is the meaning of capacity of a 63 Amps TPN MCB? Is it the per phase capacity or the totol capacity?
bit confused - am i correct in thinking that to determine line to line voltage in a star config 110v 3 phase 4 wire distribution system i would use a voltmeter? I have a circuit configured as an unbalanced load, consisting of three incandescent lamps (1x40w, 1x60w, 1x100w - all 110v rated)connected in a star configuration to a 110v 3 phase 4 wire distribution system. I want to find out what types of meters i would use to obtain: a) each line to line voltage b) the line to neutral voltage across each load c) current flowing in each line and load d) current flowing in the neutral conductor e) power supplied to the loads im assuming i would be using ammeters in series along each line and voltmeters in parallel across each line to neutral? Also how could i predict these meter readings before taking them and with which formulae? Any help would be greatly appreciated A.
WHAT IS MOBILE SUB-STATION? & REALLY BENEFIT IN INDIA
What is the permissible sound level for 1000kva DG set and how the sound level is calculated.
If not into production, how far did you follow the design and why did not you see it into production?
0 Answers Bharti, Havells, Intel,
Is it necessary to install Lighting Arrester on both side side (i.e HT and LT) of Transformer in a transmission substation? if yes Why on both side?
i have DEEE certificate in vinyaka misson unive rsity. is a INGNO if possible get the electrical C licences in Tamil nadu?
why ohmas low not sutable to transformer.
different types of electrical cable?
I am having 120KVA UPS,which is connected to DG & normal power. What is the power drawn by this system when system is running on DG ????
If one ct is reversely connected in Y system what will effect in kwh and kvarh meter?
What is the basic difference between 90% stator earth fault and 100% stator earth fault, and its phenmenona?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)