Dear Sirs,
I am a technical persons.In one of our Electrical Sub-
Station, We have installed three numbers of
1250KVA ,11KV/0.415KV Transformer to feed the Factory load.
We have found some abnormality. In one of our Transformers
the leakeage current from transformer body to earth through
earth continuity wire is almost 86 Amp but in other
transformer it is (5-10)Amp. where the load current on
three phase and neutral are respectively
1360Amp,1400Amp,1370 Amp & 176Amp. So please any technical
person help me about the reasons of this situation and how
I can rectify the fault. Moreover,I have measured the earth
resistance of the Earth continuity wire which is less than
1 Ohm.
Thanks
Tapas Barua
Answers were Sorted based on User's Feedback
Answer / anadi biswas
Hi dear,
First of all tell me the condition
Are all these running parallel?If yes,then check the
individual winding to body insulation resistance with a
Multimeter.
Also you may check the transformer oil properties i.e.
dielectric strength as well in order ensure the minimum
leakages.
If individually connected , then check all the above+ the
nature of loads connected with the earthing system.
Also in all the above case check the body earthing of each
tranformer with Earth pits connected and individual earth
pits and measure the value. You will get the conclusion.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sreenu
Hi dear,
Pls check the differential relay is not working properly, if its work this problem not faced. Pls check the primary current is equal to secondary current more than 30 times to the secondary winding.
Ex; if u have 2500kva transformer gives secondary current as per designing it vl gv 3477Amps is equal to primary current. Both r matches their is no problems transformer.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
Check the insulation resistance of No. 1.Connect a voltmeter
between body and the earth and measure the leakage voltage
which is expected to be more 86V.Unbalanced currents are
also due to contact resistance .
| Is This Answer Correct ? | 0 Yes | 1 No |
Why donot sleep below the tree for night time?
why do we connect voltmeter in parallel,why not in series,and why do we connect ammeter in series why not in paprallel...
battery capacity use of made?
0 Answers JLL, Shankar Electricals,
I want to know what is the short circuit level when 8 NOS 2000 kVA, 415v, 50hZ generator connected in paraller
what you have to see after one week or month from the day of installation of transformer ?
What is the Difference between Ac Drives and Dc Drives? According to application, speed, Torque, cost, Reliability, Construction, Motor etc... Thankyou !!!
what is the difference between starter and control panel..?
what is recovery voltage & transient voltage ?
How to calculate or formula to calculate rhe power in 2 phase system ??
what is the need of capacitor in transmission lines?and how it works.
Main CT ration is 400/5, meter CT ratio is open type: -/5A. What is the Multiplying factor of the meter, considering same PT ratio.
what is relation between vector group of transformer and its load hormonics?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)