Dear Sirs,
I am a technical persons.In one of our Electrical Sub-
Station, We have installed three numbers of
1250KVA ,11KV/0.415KV Transformer to feed the Factory load.
We have found some abnormality. In one of our Transformers
the leakeage current from transformer body to earth through
earth continuity wire is almost 86 Amp but in other
transformer it is (5-10)Amp. where the load current on
three phase and neutral are respectively
1360Amp,1400Amp,1370 Amp & 176Amp. So please any technical
person help me about the reasons of this situation and how
I can rectify the fault. Moreover,I have measured the earth
resistance of the Earth continuity wire which is less than
1 Ohm.
Thanks
Tapas Barua
Answers were Sorted based on User's Feedback
Answer / anadi biswas
Hi dear,
First of all tell me the condition
Are all these running parallel?If yes,then check the
individual winding to body insulation resistance with a
Multimeter.
Also you may check the transformer oil properties i.e.
dielectric strength as well in order ensure the minimum
leakages.
If individually connected , then check all the above+ the
nature of loads connected with the earthing system.
Also in all the above case check the body earthing of each
tranformer with Earth pits connected and individual earth
pits and measure the value. You will get the conclusion.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sreenu
Hi dear,
Pls check the differential relay is not working properly, if its work this problem not faced. Pls check the primary current is equal to secondary current more than 30 times to the secondary winding.
Ex; if u have 2500kva transformer gives secondary current as per designing it vl gv 3477Amps is equal to primary current. Both r matches their is no problems transformer.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
Check the insulation resistance of No. 1.Connect a voltmeter
between body and the earth and measure the leakage voltage
which is expected to be more 86V.Unbalanced currents are
also due to contact resistance .
| Is This Answer Correct ? | 0 Yes | 1 No |
Why indicated only R.Y.B to phase.
Draw a SLD of DG distribution up to main LT panel?
What is DC power factor??
Differance between power circuit and control circuit
what is residual current....
i have applied for junior engineer 2 c&w for Guwahati RRB please send me last five year question paper
what is fault level of power system ?
How does the phase sequence controller works, how it identifies the phases? confirm working principle
what is units of resistance
What is the requirement of grounding the neutral of single phase generators on load? If the neutral is not grounded, what will be the effect?
Please sent me some previous year question papers of BSNL-JTO telecom and RRB in ELectrical Engineering to varshashahi@yahoo.com
why the supply frequency in india is 50hz?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)