is KVAR (not reverse power) relay necessary to protect from
excitor field failure on a brushless, synchroneus generator?
Some people with previos experince tell me no but the
manufacturers tell me it is designed for that purpose.
Is it that it is only necessary for brushless generators
and not the older style with the slip rings and brushes?
Answer / k.prakashchandra
Field failure makes synch gen run as induction gen drawing
large lagging KVAR from system and hence KVAR relay will
act.In older gen, there was no such relay.If the field
breaker tripped the whole unit tripped on master trip.If the
FB did not trip,the unit cb tripped on over current.
Is This Answer Correct ? | 1 Yes | 0 No |
what type of euse we should use ? 1- High resistance & low temperature 2- High temperature low resistance
State the types of distortions in amplifier?
can we use 220 volt 15 w a.c. lamp on 220 volt d.c.
sir, What is the purpose in Generating power plant is operated Lagging PF and Above 0.9 lag PF?
Can we step up a 230V supply to 400V using a single phase transformer??
Moving Iron instruments are applicable with a) DC only b) AC only c) DC & AC
14 Answers Bhel, Engineers India, Engineers India Limited,
how to compute kAIC? with formulas...
What is the difference between Zero Current Transformer and Core Balance CT ?
Piezoelectric materials serve as a source of:- A. Microwaves B. Ultrasonic waves C. Musical waves D. Resonant waves
. Draw the vector diagram and condition for the following: 1) Dyn1 2) Ynd0 3) YnYn0
What is the reason of polyphase induction motor tripping suddenly on high current during running at 70% laod? Motor IR , winding resistance & inductance balance. Motor no load current is balance and ok as per mgfr. data.
Why the electron flow in reverse of current.