what are the standard values for resistances(Megger testing)
between L&N, L&E and N&E (L=Live,N=Neutral, E=Earth)?
Answer / pswin
You ask the value between L,N and E. So I will assume that you will test for single phase and the test voltage must be 500 v scale and full scale is 100 mega ohm.Minimum value should be 0.5 mega ohm between each conductors. If lower than that value, the cable or wire is not certified to use. For three phase, above answer is acceptable,too.
| Is This Answer Correct ? | 16 Yes | 3 No |
circuit breaker work alone during fault condition or need any relays ?
A 2083kva AVR was tested, phase to ground shows continuity, what is the implications
how we can varying the speed of dc motor ?
what is the static device rather than xmer which work on same principle as xmer?
why we can't use more then 50 hz in india ? Is it possible ?
what is the difference withbeen lighting capacitor and motor capacitor?
resitance in ac=1.6*resistance in dc
what is meant by dedicated earthing?
hopkinson's test
I decided to provide a 11KV / 440V Xformer in my Substaion. What are the protection required for that?
if our load in 3 phase circuit is 4000 amp. calculate the capacity of capacitor panel if line power factor is.80 .
During regenerative breaking= A rotating magnetic field is reversed B slip is positive C torque is positive D slip is negative
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)