if we want ot select cable size with reference to load
current it take than what is the formula and it is same for
aluminium or copper?
Answers were Sorted based on User's Feedback
Answer / mahesh sali
while selection of cable u should followed the below steps ;
1) cal. the full load current If.L= ( kw / 1.732 x v x
p.f. )
Assume the voltage drop of system as per application says
for motor it should be 10% Vd = 10%
2) Vd = ( 10/100) * v
3) Vd/ph. = ( Vd/1.732 )
4) R = vd/ph./IF.L
5) R-Rho*L/A
Assume , for Copper cable Rho = 1.72 e-8 Ohm-m
L = Length of cable
Base on the above assumation u can easily cal. the size of
cable.
After cal. the cable size , add. 25% extra in ur cal. the
cable size .
Thanking u
| Is This Answer Correct ? | 2 Yes | 0 No |
In case of transformers, for copper cable 2.5A/sq mm and Al
i.5A/sq mm ,for generators 1.5A/sq mm and 1 A/sq mm
respectively.For others 4A & 2.5A per sq mm
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / naveen perugu
for copper cable 4Amps/Sqmm is the standard practice and
for alluminium 3Amps/sqmm is the standard practice for
safer operations
| Is This Answer Correct ? | 4 Yes | 8 No |
What will be the voltage impact on secondary side of two transformers with different vector groups when both voltages are compared.
how to calculate KA rating of C.B?explain with Formula.
What will happen if the oil level in the buchholz realy of a transformer gets down?
Is there any local or International standards that prohibit the installation of earthing pit in the planters area where the earthing pit is subject to continues soak in water?
I want formula to calculate cable size as per load given in length & amp. I searched many sites but didn't right answer. Please reply me asap.
what will happen if delta - star , 400V to 6.6KV step up transformer neutral is not grounded, Neutral is not used but transformer is provided with neutral.
Whats the minimum value for I.R. that can be allowed for HT & LT alternators for operation?
EXPLAIN WORKING PRINCIPLE OF ALTERNATOR & MOTORS.
What does bode plots shows?
If I need to purchase a step-down transformer (from three phase 33kV 50Hz to 400/230V), what additional information do I need from the main supply power line?
why generator and t/f ratings given in kva?
The insulation resistance of a cable can be measured by
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)