if we want ot select cable size with reference to load
current it take than what is the formula and it is same for
aluminium or copper?
Answers were Sorted based on User's Feedback
Answer / mahesh sali
while selection of cable u should followed the below steps ;
1) cal. the full load current If.L= ( kw / 1.732 x v x
p.f. )
Assume the voltage drop of system as per application says
for motor it should be 10% Vd = 10%
2) Vd = ( 10/100) * v
3) Vd/ph. = ( Vd/1.732 )
4) R = vd/ph./IF.L
5) R-Rho*L/A
Assume , for Copper cable Rho = 1.72 e-8 Ohm-m
L = Length of cable
Base on the above assumation u can easily cal. the size of
cable.
After cal. the cable size , add. 25% extra in ur cal. the
cable size .
Thanking u
Is This Answer Correct ? | 2 Yes | 0 No |
In case of transformers, for copper cable 2.5A/sq mm and Al
i.5A/sq mm ,for generators 1.5A/sq mm and 1 A/sq mm
respectively.For others 4A & 2.5A per sq mm
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / naveen perugu
for copper cable 4Amps/Sqmm is the standard practice and
for alluminium 3Amps/sqmm is the standard practice for
safer operations
Is This Answer Correct ? | 4 Yes | 8 No |
what is the difference between Ith & Iu rating in MCCB. Particularly on SACE ABB Circuit Breaker?
How to covert the ac to dc and how to control the dc output?
when we start the tube light, then it takes initially 1100 volt, after glow it takes 120 volt?(when we give 220 volt a.c.)
In stepdown transformer 11/415 volt two nos.(R & Y)HT side fuse is blown ,what will be voltage of ry,rb,yb in secondary side
why is the size of earth conductor is half of phase conductor.
1 Answers Century Pulp and Paper, L&T,
Between rotating armature type and rotating field type arrangements which one is adopted for large rated alternators and DC generators.Why there is difference in the choice?
whit is 33kv power 300*300 cable full current with formula
why measure the gravity in battery?
Hi,i want to appear for IES (EEE),can any one plz help me how to apply and how to prepare
if the armature current in a dc generator is ac ( sinusoidal ) why doesnt the sjhape af armature mmf a sinusoidal (ni) ? armature mmf in case of a dc machine is triangular.
wat is the difference between real power and reactive power..which is useful..?and how it s useful..wat is the effect of these on a power system...
Is there any problem if i connect APFC panel in generator circuit