Answer / mahesh sali
while selection of cable u should followed the below steps ;
1) cal. the full load current If.L= ( kw / 1.732 x v x
p.f. )
Assume the voltage drop of system as per application says
for motor it should be 10% Vd = 10%
2) Vd = ( 10/100) * v
3) Vd/ph. = ( Vd/1.732 )
4) R = vd/ph./IF.L
5) R-Rho*L/A
Assume , for Copper cable Rho = 1.72 e-8 Ohm-m
L = Length of cable
Base on the above assumation u can easily cal. the size of
cable.
After cal. the cable size , add. 25% extra in ur cal. the
cable size .
Thanking u
| Is This Answer Correct ? | 2 Yes | 0 No |
In case of transformers, for copper cable 2.5A/sq mm and Al
i.5A/sq mm ,for generators 1.5A/sq mm and 1 A/sq mm
respectively.For others 4A & 2.5A per sq mm
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / naveen perugu
for copper cable 4Amps/Sqmm is the standard practice and
for alluminium 3Amps/sqmm is the standard practice for
safer operations
| Is This Answer Correct ? | 4 Yes | 8 No |
what the function breaker failure scheme, how is it operated
What is the unit of inertia constant of rotating machines? Which has more inertia constant between turboalternator and hydroaltermanor and why?
Why MCCB is Getting tripped sometimes when there is no load in the Midnight ?
protection used for alternator , feeder , transmission line
what is the meaning of impedance protected in instrument cooling fan
Explain Continuous and Discrete signals?
what is phase angle ? and also tells me why my phase-phase voltages are 390 rather then my single phase voltages are 221 and 223 respectivly?
explain which quantities change in the starting and the and the running condition in induction motor
how the find ct mf and mf roll in metering
why current flows from +ve to -ve terminal
Why secondary of a CT in a power system acts as an open circuit after core saturation?
HELLO EVERYONE, I RECENTLY HAVE FOUND ONE PROBLEM, I WAS TAKING NO LOAD TRIAL OF AN HT MOTOR 920 MOTOR , 1440 RPM , 6.6 KV, WITH AUTO TRANSFORMER. AT 450 V, LOAD WAS 40 AMP AND SPEED WAS 250 RPM. BUT AS WE INCREASE VOLTAGE FROM 450 TO 480V, LOAD BECOME 41 AND SPEED REDUCED TO SOME RPM . SO WHICH PHENOMENON ACTED HERE FOR REDUCING SPEED.?? AND IS IT HAPPENING ALWAYS OR IT IS RARE? I ALSO HAVE FACED SUCH PROBLEM WITH FEW LT MOTOR ALSO.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)