what is the load amp for 1 HP 3 phase Motor ?
Answers were Sorted based on User's Feedback
Answer / chethan
V=415 ,cos=0.8
1HP = 746 Watts
p=1.732*V*cos*I
746=1.732*415*0.8*I
I=746/575.025
Ans.1.297
Is This Answer Correct ? | 72 Yes | 17 No |
Answer / prasant
V=415V ,cos=0.8
1HP = 746 Watt
p=1.732*V*I*cos
746=1.732*415*0.8*I
I=746/575.025A
Is This Answer Correct ? | 26 Yes | 12 No |
Answer / md nawaz
what is the load amp for 1 HP 3Phase Motor?
= HP/Root 3*V*I*Cos,
I=?
1 Hp=746 watt,
I=746/1.732*415*0.8,
I=746/575.024,
I=1.29amps,,,,,,,
1hp=1.29amps
Is This Answer Correct ? | 22 Yes | 8 No |
Answer / karan
the thumb rule is,I= H.P*1.5
but current depend on Power factor,
Example power factor is 0.85
1 H.p=750kw=Root3*V*I*cosQ=1.73*415*I*0.85
so I=750/1.73*415*0.85=1.23 Amp
when pf is 0.80 then I=1.30
when pf is 0.95 then I=1.09
Is This Answer Correct ? | 17 Yes | 7 No |
Answer / rahulsinh chavda
Can anyone please expain me how the answer is 1.5amp?
Is This Answer Correct ? | 11 Yes | 3 No |
What is the need for a controller?
We order Dyn 5 distribution transformer to a company. What arrives is Dyn 11. Is it ok to use this transformer. It will be installed alone.
what is the difference between linear choke and suction choke?
two bulbs of 100w and 40w respectively connected in paralel across a 230v supply.which bulb will glow bright and why?
lamination figures
why the transformer connected like STAR- STAR, DELTA- DELTA, STAR- DELTA, DELTA-STAR ...? why these connections ,,, explain the advantages these connections?
How do we arrive at selecting reactive capacitance value as 30% of h.p rating of motor?
Whether earthmat designning is done only for sub station or it can be done for multy residential complexes also? What is the size, type & arrangement of the earth grid to be done?
Which are resistive loads & which one are inductive loads : Refrigerator, Split air conditioner, ceiling fans, well pump, fluoresecent bulbs, T.V, CRT Monitors, Adsl Routers, C.P.U, Printers, Deep Freezers, Speakers, DVD Players, Microwave oven etc. ? Output Power for these Appliances Would be same like this : P = V * A * P.F Or would be changed ? thanks
what is the reason for balance of voltage in magnetic balance test?
Is there any scope for an electrical engineer in MRF company......
why we oltc on hv side of tranformer only