Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why we remove capacitor connection in 3 ph Induction Motor
while taking noload test.

Answers were Sorted based on User's Feedback



why we remove capacitor connection in 3 ph Induction Motor while taking noload test...

Answer / loboreliance2003

Actually the question should be why is the capacitor bank
connection to be removed from the motor before taking the
no load test. This has nothing to do with capacitor of
motor. 3Ph induction motors dont have capacitors to
start.These are only used for single phase motors.

The answer is that capacitor bank is provided on any
Inductive load due to power factor dipping to below0.8 and
sometimes even to 0.5. To improve the power factor we have
to connect the capacitor banks depending on the size of
motor.

But if motor is not run on load then it is not necessary to
connect the capacitor. Hence no load tests can be done
without having to connect the capacitor bank to the motor.

the other reason is that there is danger of over voltage
due to capcitor being connected then PF will be greater
than 1 which could damage the motor windings. I have faced
these motor burning problems due to this reason.

Is This Answer Correct ?    8 Yes 2 No

why we remove capacitor connection in 3 ph Induction Motor while taking noload test...

Answer / mukesh.k.sharma

plz send me ans on my mail id
mukesh.k.sharma@adityabirla.com

Is This Answer Correct ?    5 Yes 2 No

why we remove capacitor connection in 3 ph Induction Motor while taking noload test...

Answer / baskaran

no need to capacitor in 3phase induction motor.
if capacitor used means improve the powerfactor only..

Is This Answer Correct ?    3 Yes 1 No

why we remove capacitor connection in 3 ph Induction Motor while taking noload test...

Answer / abhinav

i am not seen 3 phase induction motor require capasitor.

Is This Answer Correct ?    3 Yes 2 No

why we remove capacitor connection in 3 ph Induction Motor while taking noload test...

Answer / mas tachnocrat

hmm 3 phase inductin motor needs a capacitor; to improve
power factor or if u want to start 3 phase induction motor
from 2 phase
or noload test main capacitor kya kare gaa

Is This Answer Correct ?    2 Yes 2 No

why we remove capacitor connection in 3 ph Induction Motor while taking noload test...

Answer / raju

3 ph induction motor doesn't require any capacitor.in 1 ph induction motor require capacitor to divide a phase into two (as per double revolving field theory)so there is no need of capacitor

Is This Answer Correct ?    1 Yes 1 No

why we remove capacitor connection in 3 ph Induction Motor while taking noload test...

Answer / ramesh

i also face this ques pls send the ans

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

Isolation transformer primary to sec turns ratio?

2 Answers  


In scott connected transformer number of turns in the primary winding of teaser transformer is % of number of primary turns of main transformer A 86.6 B 57.7 C 14.4 D 33.3

1 Answers  


what will happen if secondary of potential transformer (220kv/110volt) of any metering core or protection core (cables) of any phase got earthed??

1 Answers  


what is the function of bearing in dc mchine" and where it is placed

0 Answers  


What is the basic difference among Circuit breaker,Contractor and Isolator? Are they different names of same device/equipment?

2 Answers  


why the name mho relay,despite the locus of circle is impedance?

1 Answers   KSEB,


I want formula to calculate current loss with distance in km.I searched many sites but didn't right answer.Plz reply me

0 Answers   SECL,


what is the rating of power generation in india?

10 Answers   Siemens,


IN MY INDUSTRIES 125 HP MOTOR USED FOR THAT ONLOAD AMPS UP TO 280 SO CAN I USE ONE LOWER KVA DG SET WITH STEP UP TRANSFORMERS THAT MEANS WITH LOW POWER INPUT TO GET CONSTANT HIGH POWER OUTPUT EG:125KVA DG SET = 250 KVA STEP UP TRANSFORMERS

1 Answers  


My switchgear busbar is rated at 2000A and just imagine the actual load on busbar is 1000A. From that busbar there are 10 outgoing feeders. Now the question is will the load be 1000A on each outgoing feeder or 100A per outgoing feeder. 2nd thing how do i calculate the load on individual feeder. Thanks for your time. Please provide some clarification on this issue.

1 Answers   Alstom,


what is the difference between the voltage of 5 volts capacitor and and 5volts battery?

0 Answers  


when generator of a power plant is not connected to grid , by increasing the mechanical torque speed of rotor increases but when it's connected to load instead of increase in speed current increases , why?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)