Can we use HRC fuse inplace of semi conductor fuse ? What
are difference between them?
Answers were Sorted based on User's Feedback
Answer / rct
no ,semiconductor fuses are fast acting used for switching
devices such as transistors,IGBT,thyristors in order to
protect them.The rupture time is in msec .HRC fuses rupture
time is more and the current for rupturing is also high
making it suitable for motors/resistive loads
Is This Answer Correct ? | 48 Yes | 0 No |
Answer / thiagarajan.e
No we should not use the hrc fuse in place of semiconductor fuse.Because the hrc fuse will act ,at the time of short circuit or the current exceeding the fuse limit.But the semiconductor fuse will act when the current exceeding as well as no current in the circuit,where the voltage exceeds the fuse limit.So on any instant we will not match each other.
With best regards,
Thiagarajan.E
Is This Answer Correct ? | 10 Yes | 0 No |
Answer / thileepan
s ofcourse we can use it........because it can be used for both high current and low current purpose.....HRC ll be indicated in MVA.....but here the full capacity of current i.e rated mva.........becuse it ill melt the fuse element before reaching rated mva due to its cut off charecteristics...
Is This Answer Correct ? | 0 Yes | 32 No |
What is the max value of neutral current that can be allowed in system?
What do you mean by per capita requirement of electrical energy in india
will aqatic animal die if we ground the wire of three phase instead of grounding to earth
what is the use of spherical metal balls attached on to the earth wire of transmission over head lines?
What is the Total Power generation Capacity in India at present ??
20 Answers Bhel, College School Exams Tests, IBM, NTPC,
WHY IS THE NO LOAD CURRENT SMALL FOR A TRANSFORMER COMPARED TO OTHER ROTATING ELECTRICAL MACHINES??
how we decide wire gauge for ac or dc coil and what is the basic diff. B/w these two coil?
Which pump set is more suitable and economical for liftingwater from 300Mtr borewell? A. Compressor Pump B. Submersible Pump C. Jet Pumps D. 25HP Centrifugal Pump Q. from PSC Test 22-11-2008 Meter reader
why not phase to phase fault occure in raining day in hv sub-station?
1.Can we use 6.6/11KV 300sq mm xlpe 3core cable for LT use (415 Volt). 2. If we use it for LT then what is the current rating
Why do we choose 33kV transmission for industrial purpose and 11Kv for township?
i've iocl interview.. if you know the interview process please give me information..