Can we use HRC fuse inplace of semi conductor fuse ? What
are difference between them?
Answers were Sorted based on User's Feedback
Answer / rct
no ,semiconductor fuses are fast acting used for switching
devices such as transistors,IGBT,thyristors in order to
protect them.The rupture time is in msec .HRC fuses rupture
time is more and the current for rupturing is also high
making it suitable for motors/resistive loads
| Is This Answer Correct ? | 48 Yes | 0 No |
Answer / thiagarajan.e
No we should not use the hrc fuse in place of semiconductor fuse.Because the hrc fuse will act ,at the time of short circuit or the current exceeding the fuse limit.But the semiconductor fuse will act when the current exceeding as well as no current in the circuit,where the voltage exceeds the fuse limit.So on any instant we will not match each other.
With best regards,
Thiagarajan.E
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / thileepan
s ofcourse we can use it........because it can be used for both high current and low current purpose.....HRC ll be indicated in MVA.....but here the full capacity of current i.e rated mva.........becuse it ill melt the fuse element before reaching rated mva due to its cut off charecteristics...
| Is This Answer Correct ? | 0 Yes | 32 No |
Explain Active power,reactive power,how its related to each other , & inductive ,capacitive.
what is phase and neutral.
A ii kv 1200 A Breaker combination fixed in a cubicle. How many ampere Fuse is required? If fuse is not using, Why?
1. What is the exact formula for one weber? for example,(one ampere = one coulomb electron of electrons crossing a point of conductor at one second. i.e, 1A=1Q/1sec)
WHAT MEANT BY SEVICE FACTOR?
what is fuction static switch in ups and tell me use parts name and fucion
What is the difference between diode and a transistor in terms of the direction of current flow?
What is the stander resistance value between the neutral and earth?
10 Answers Crossdomain, Sepco,
3-PHASE 15KVA dg IS EQUIVALENT TO 12 KW,hOW?
What is d diff. btw MCB & MCCB???
A 11 KV motor is working. if the supplay is fail. what will happened with it's breaker? Trip / remain the same condition?
Why most of analog o/p devices having o/p range 4 to 20 mA and not 0 to 20 mA ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)