without any theoretical calculations, can u approximately
tell the current rating of a motor(above 30hp)working at 415VAC.
Answers were Sorted based on User's Feedback
Answer / venu
As per thumb rule the current rating of a motor working at
415vac
equals to double the KW rating (and -2% of double the KW)
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / shahid
Thumb rule to calculate the current of all d LT ac motors
is:
A = 1.7*KW
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / azarudeen
Above 40A (if efficiency of motor - 90% & PF - .8)
FORMULA: I = (HP*746)/(1.732*415*Eff*PF)
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / dheeraj soni
As per thumb rule motor working at 415 ac their current
rating is aprroximately 1.5 times of its HP Rating
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / arsenal
actually how is the thumb rule obtained......is there any
derivation.........
| Is This Answer Correct ? | 0 Yes | 0 No |
As per the Thumb Rule,
Current = (Motor HP x 1.5)-10% of the total
Example: If we want to calculate the current of the 100Hp
motor then
current = (100 x 1.5)-10% = 150-15 = 135 Amp.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / m. madhu sudhanarao
As per thumb rule Motor current rating at 415AC is
approximately 1.6times the KW rating.
| Is This Answer Correct ? | 0 Yes | 1 No |
How to find Cable size? Caterpillar generator produce (Two generators) 127*2=254 amp at 11 kv . What would be the cable size (XLPE) to supply 256 amp at 11 kv? Air or surrounding Temperature is 32 degree C. Cable will go under ground at 2.5 feet depth. Group Rating Factors is 3 cables. Clearance between cables is 7 cm. Soil Temperature (Ambient) 28o C Soil Thermal Resistivity is 1.2 K.m/W I would like to use 3 separate single core instead of using 3 core cable. Some says I should use three separate single core 120RM cables. Some says 70RM .some says 95. I m totally confused. Is there ant specific rule to determine cable size? What would be the LT cable size to flow 500 Amp current? Ifte My e mail address is ifte13@yahoo.com Anyone please send me the answer to my e mail address, i will be very glad.
Are Refrigerators & Deep Freezers the Inductive load ? How to calculate the Power Factor & hence the Output Power for them ?
I have experienced electrical maintenance HT ,but I completed be ECE ....can I apply c license or not ???? Pls help me friend s...
what do you mean electrical earth pit?
What are differences between Conventional & Addressable type smoke detectors?
What is the alternate solution for testing of polarity by using polarity tester while its milli ammeter does not works?
how much percentage set in transformer diffrencialrelay
Do you know how to maintain a generator, if so what are those maintenances?
Why 1500 rpm of deasel generator please explain to me?
1 Answers Integral BioSciences,
Can I use distributon class/transmission class Lightning arresots for protecting the building? If not why please explain?
Transformer cores are laminated in order to A simplify its construction B minimize eddy current loss C reduce cost D reduce hysterisis loss
How can we calculate the current if we have load in KVA and if the load in KW then what formula will be use for calculating the current. please give both the formula for calculating the current.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)