Why the transformers are rated in kva?
Answers were Sorted based on User's Feedback
Answer / r
the losses depends purely on voltage and current . that is
core loss is proportional to voltage and cu loss is
proportional to current, thats why the tr is rated in KVA
not in KW
| Is This Answer Correct ? | 37 Yes | 6 No |
Answer / s s nanal
Transformer is AC Static Inductive M/c where there are no
moving parts.Hence frictional losses are nil.In AC M/cs
power factor i.e.cosine of angle between voltage & current
is important.The relation between KVA & KW is given by
following formula. KVA = KW /P.F. or KW = KVA X P.F. This
angle between Voltage & current decides actual power
available.Transformer being highly inductive m/c power
factor is never = 1.Hence actual KW available is always
less than KVA. Hence X'mers are rated in KVA.
| Is This Answer Correct ? | 13 Yes | 4 No |
Answer / ashok
because of there are two type of loses in transformer one is iron loss and second is copper lose.iron lose is proportional to the voltage and copper lose is depends upon current hence transformer losses is measured in KVA.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / vivek
and yes , one more thing the output of a transformer has no
realtion to the power factor of the load , ie the active and
reactive loading of a transformer can be done in any range
as long as the combined active and reactive loading does not
exceed the max current limit . this will also give you the
answer to why motors are rated in KW , as the power output
of a motor is dependent on only the active power it consumes
.....
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / sathish.b
the losses depends purely on voltage and current . that is
core loss is proportional to voltage and cu loss is
proportional to current, thats why the tr is rated in KVA
not in KW
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / vivek
the limiting factor in transformer loading is voltage and
current , so , specifying a transformer in KVA with a given
primary and secondry voltage gives he maximum loading
current in both the sides. coupled with the transformer base
impedence , it also gives the regulation and losses at any
load .
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / engr. tariq
KW = KVA * PF
According to this formula since power factor depends on
load or load current( Apparent /Real power ) therefore we
can say that the rating of transformer is in KVA.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / mijibar rohaman
kva=kw/p.f
as pf never more than unity,so it can be varied with the
angle between voltage and current.so kw alsom may be
varied.as a result tranformer is rated as kva.
| Is This Answer Correct ? | 1 Yes | 1 No |
different between highvoltage & lowvoltage source
Thermal withstand capability under full short circuit conditions, in terms of number of times of occurrence of short circuit and corresponding anticipated percentage reduction in transformer life.
hi pal, i am vengatesh from tamilnadu(chidambaram),i have called for the written test for the post of jr executive(ELECTRICAL) of AAI ,I dont know about the question paper pattern,so any kindly help me to face the examination,post me the model question papers and some tips to write my examination to (vengi.annadurai@gmail.com)
arrange to send solved question and answer its easy to study and understand the thing, because of Exam is to be conducted shortly
Is HT capacitor rating connected directly to motor terminals , related to motor no load current?
how we can select a transformer based on a particular load. suppose we have 4 motors of rating 40 h.p , 50 h.p, 80 h.p & 100 h.p. then what rating of transformer we can select. urgent. pls reply
Where is the center of magnetic field in alternator
what is the difference between NC & CNC machine.what is the difference between equipment & machine tool
When a square wave is applied to primary of a transformer then what will be output wave form of secondary ?
what is positive,negative and zero sequence in power system?
how to difference between the HT< cables
What is the resistance of the field winding of a d.c. Shunt generator kept low?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)