How to calculate cable sizes in sq.mm. with using motor KW?
Any formula there?
Answers were Sorted based on User's Feedback
Answer / abid
Normally for the circuit breaker calculation we multiply our motor's current into 125% for example if a motor 5HP operates in 8amps we multiply8*125%(10) so the breaker size will be 8+10 18amps or 20 amps.
and for the cable size we multiply breakers amp*1.5
=27
so for 5hp 3ph motor suitable breaker is 20amps
and the suitable cable 4sqmm
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / naresh
1sqmm will withstand upto 4amps.
(i.e) 1sqmm = 4amps
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / sibu
One has to consider the distance of the motor and power supply sources too. In short if the motor distance is let say 400 meters from the power supply then voltage drop will be more and in that case u need to consider bigger size cable then what u find in calculation
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.l.lim
ex 10kw 3 phase ac motor,
10kw x 1.74 = 17.4 amp
MCB using 25 amp/30 amp 3 pole(C)
Motor using star-delta/overload setting 0.58 = 10.1 amp
cable size = 6x2.5mm2/1c pvc copper cable
if using soft starter
MCB using 25amp/30amp 3 pole MCB(C)
cable size = 3x4mm2/1c pvc copper cable
cable size :calculate include starter overload setting
(right or wrong,thank's)L
| Is This Answer Correct ? | 17 Yes | 20 No |
Answer / pedro
what's wrong with you guys. You dont even know how to spell
correctly. Please improve on that. Its not only about idea
but also on how you convey it. Damn!
| Is This Answer Correct ? | 6 Yes | 16 No |
Answer / raja
THE ABOVE SAID IS WRONG , ITS A THUMB RULE I USE TO FALLOW
1 sqmm = 5A & endangering amps withstand is 8A for alu
(sqmm * 1.87A)for cu sqmm *2
| Is This Answer Correct ? | 25 Yes | 44 No |
Answer / hemant
Normally copper has more conductivity than aluminium. So it
is actually reverse. 1.5 mmsqr for copper and 2.5 mm sqr
for alu
| Is This Answer Correct ? | 47 Yes | 89 No |
Air refrigeration cycle works on the
what are the main parts of UPS what is the function of that?
23 Answers Apollo, HCL, Liebert, Royal Furnishers, Tech Mahindra,
why surge suppressor in vaccum circuit breaker and it is only in motor feeder why not in tranformer feeder?no surge suppresor in ocb in motor feeder?
What will happened if the neutral of the (star connected secondry) Xformer disconnected? (if its Above KVA rated one)
what is the difference between earthed cables and unearthed cables
why ht motor connection in star
Resistor switching is used in which type Circuit Breaker ? a) oil filled CB b) Air blast CB c) Gas filled CB
11 Answers Engineers India Limited, wbsedcl,
Is 3 phase induction motor can work as a generator?? if so why & how??
what is relation between HP & BHP
what is meant by the phrase 'static load' in case of shorting in a generator excitation system?
what is the function of capacitor duty contactor in an capacitor panel???
What is mean by spike arrester(Voltage Operated)
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)