Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to calculate cable sizes in sq.mm. with using motor KW?
Any formula there?

Answers were Sorted based on User's Feedback



How to calculate cable sizes in sq.mm. with using motor KW? Any formula there?..

Answer / abid

Normally for the circuit breaker calculation we multiply our motor's current into 125% for example if a motor 5HP operates in 8amps we multiply8*125%(10) so the breaker size will be 8+10 18amps or 20 amps.
and for the cable size we multiply breakers amp*1.5
=27
so for 5hp 3ph motor suitable breaker is 20amps
and the suitable cable 4sqmm

Is This Answer Correct ?    3 Yes 0 No

How to calculate cable sizes in sq.mm. with using motor KW? Any formula there?..

Answer / naresh

1sqmm will withstand upto 4amps.

(i.e) 1sqmm = 4amps

Is This Answer Correct ?    3 Yes 0 No

How to calculate cable sizes in sq.mm. with using motor KW? Any formula there?..

Answer / sibu

One has to consider the distance of the motor and power supply sources too. In short if the motor distance is let say 400 meters from the power supply then voltage drop will be more and in that case u need to consider bigger size cable then what u find in calculation

Is This Answer Correct ?    1 Yes 0 No

How to calculate cable sizes in sq.mm. with using motor KW? Any formula there?..

Answer / k.l.lim

ex 10kw 3 phase ac motor,
10kw x 1.74 = 17.4 amp
MCB using 25 amp/30 amp 3 pole(C)
Motor using star-delta/overload setting 0.58 = 10.1 amp
cable size = 6x2.5mm2/1c pvc copper cable

if using soft starter
MCB using 25amp/30amp 3 pole MCB(C)
cable size = 3x4mm2/1c pvc copper cable

cable size :calculate include starter overload setting
(right or wrong,thank's)L

Is This Answer Correct ?    17 Yes 20 No

How to calculate cable sizes in sq.mm. with using motor KW? Any formula there?..

Answer / pedro

what's wrong with you guys. You dont even know how to spell
correctly. Please improve on that. Its not only about idea
but also on how you convey it. Damn!

Is This Answer Correct ?    6 Yes 16 No

How to calculate cable sizes in sq.mm. with using motor KW? Any formula there?..

Answer / raja

THE ABOVE SAID IS WRONG , ITS A THUMB RULE I USE TO FALLOW
1 sqmm = 5A & endangering amps withstand is 8A for alu
(sqmm * 1.87A)for cu sqmm *2

Is This Answer Correct ?    25 Yes 44 No

How to calculate cable sizes in sq.mm. with using motor KW? Any formula there?..

Answer / ibrahim

for cooper 2.5 mm for 1 amp
for aluminum 1.5 mm for 1 amp

Is This Answer Correct ?    11 Yes 30 No

How to calculate cable sizes in sq.mm. with using motor KW? Any formula there?..

Answer / hemant

Normally copper has more conductivity than aluminium. So it
is actually reverse. 1.5 mmsqr for copper and 2.5 mm sqr
for alu

Is This Answer Correct ?    47 Yes 89 No

Post New Answer

More Electrical Engineering Interview Questions

What is the maximum breakdown voltage of 11KVA and 66 KVA power line and how it is calculated?

0 Answers   Anglo Platinum, Narnarayan Electrical,


If we have two nodes A and B and Vab is the potential difference between these nodes then which node is called reference node a.node A b.node B c. Ground node

1 Answers  


what is High resistance grounding and whatis the criteria for the selection of High resistance grounding

1 Answers   MAHINDRA,


why insulation cost is more in underground cable than in overhead line?

2 Answers  


What is the difference between generator and turbo generator - related to power gereration

1 Answers  


Whether the LIGHTNING is AC or DC?

9 Answers   Bhel, IEEE,


Dear all, how we select the cable size according  to current with or without including different correction factor , is there any direct method for sizing of cable... 

0 Answers   Kharafi National,


WHAT IS MEANING OF VECTOR GROUP FOR TRANSFORMER

2 Answers  


what is the mean of"turbo" in turbo alternator???

1 Answers   CCCL,


RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV is ok ,but haw to calculate the KA rating?

0 Answers  


Differnce between earthing and nuetral

3 Answers   S Tech, wbsedcl,


Can transformer develop three phase power from a single phase source?

12 Answers   ONGC,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)