Answer / vishwas bhat
the minimum distance two earthpits should be twice the
length of the earth electrode used i.e. for example
distance between 2 3meters pit will be 6mts.
| Is This Answer Correct ? | 130 Yes | 17 No |
Answer / vishwas bhat
distance between two pits should not 3m bcoz there is a
tecnical reason behind it, and the reason is that when
there is some heavy earth fault and if one of the pits is
acting as a returning path for earth fault current then it
might go dry due to heat dissipation by the passing
current, and simultaneously one more heavy fault happens
then these pits will offer high resistance because they
have lost moisture and which is not desirable, hence the
distance between two 3m pits should be minimum 6mts.
| Is This Answer Correct ? | 67 Yes | 12 No |
Answer / devesh mishra
The distance b/w the pits depends on,
a)Type of earthing
b)Type of Soil
In normal practise ,for solid earthing,the distance b/w the pits should be 3 mts.
| Is This Answer Correct ? | 60 Yes | 19 No |
Answer / s .mariappan psr
The minimum distance of two earth Pit is two pit no of Earth electrode(Rod , Pipe , Plate).For example
1st earth Pit electrode - 3m
2nd earth Pit electrode - 3m
our two earth pit distance- 3+3=6m
According to your electrodes and requirements
| Is This Answer Correct ? | 19 Yes | 6 No |
Answer / mahesh
WHAT IS THE DISTANCE BETWEEN BODY EARTH PIT AND NEUTRAL EARTH PIT?
| Is This Answer Correct ? | 16 Yes | 9 No |
Answer / pramod sharma
according to bis 3043 1987 one earthing to another distance minimum 3 mtr techinacl reason is if earthing distance lass than 3 mtr than surface area is overlaping and fault curreent desipate to earth. also depend soil restivity and appplication load
| Is This Answer Correct ? | 10 Yes | 4 No |
Answer / harkamal singh
1)Distance between two earthing pit depending upon soil resistance.
2)Type of earthing
3)earth fault calculating.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / vel
As per IS3043:
Distance between plate earth electrodes shall be 8 m minimum.
Distance between pipe earth electrodes shall be 5 m minimum.
| Is This Answer Correct ? | 14 Yes | 19 No |
which type of effect of turbine and generator reverse power protection ?
where used impendence relay?
What is time invariant system?
What will be the size of copper cable (each for 3 phase and 1 neutral) from Service connection Kit-Kat to Panel Board (i.e. to main switch) for a 6 pole 3-phase AC induction motor of 200 H.P. capacity? Amp-255 A, Frequency:- 1450 rpm.
what is difference between di electric and insulator?
what will happen when excitation of a synchronous machine is suddenly reduce to zero when it is running at full load..??
Power Factor Correction Panel (Manual & Automatic)
State norton’s theorem?
What is the suitable transmission voltage?
How to check VFD outgoing voltage
what is meant by directional earth fault and non directional earth fault? describe both.
In control room of our one plant there is a continuously the incoming power goes to PC is vary,means in stabilizer it continuously indicate from high input to low and low input to high. what is the reason and its solution.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)