what should be distance between two electrical earthing pit
as per i.e.e
Answers were Sorted based on User's Feedback
Answer / vishwas bhat
the minimum distance two earthpits should be twice the
length of the earth electrode used i.e. for example
distance between 2 3meters pit will be 6mts.
| Is This Answer Correct ? | 130 Yes | 17 No |
Answer / vishwas bhat
distance between two pits should not 3m bcoz there is a
tecnical reason behind it, and the reason is that when
there is some heavy earth fault and if one of the pits is
acting as a returning path for earth fault current then it
might go dry due to heat dissipation by the passing
current, and simultaneously one more heavy fault happens
then these pits will offer high resistance because they
have lost moisture and which is not desirable, hence the
distance between two 3m pits should be minimum 6mts.
| Is This Answer Correct ? | 67 Yes | 12 No |
Answer / devesh mishra
The distance b/w the pits depends on,
a)Type of earthing
b)Type of Soil
In normal practise ,for solid earthing,the distance b/w the pits should be 3 mts.
| Is This Answer Correct ? | 60 Yes | 19 No |
Answer / s .mariappan psr
The minimum distance of two earth Pit is two pit no of Earth electrode(Rod , Pipe , Plate).For example
1st earth Pit electrode - 3m
2nd earth Pit electrode - 3m
our two earth pit distance- 3+3=6m
According to your electrodes and requirements
| Is This Answer Correct ? | 19 Yes | 6 No |
Answer / mahesh
WHAT IS THE DISTANCE BETWEEN BODY EARTH PIT AND NEUTRAL EARTH PIT?
| Is This Answer Correct ? | 16 Yes | 9 No |
Answer / pramod sharma
according to bis 3043 1987 one earthing to another distance minimum 3 mtr techinacl reason is if earthing distance lass than 3 mtr than surface area is overlaping and fault curreent desipate to earth. also depend soil restivity and appplication load
| Is This Answer Correct ? | 10 Yes | 4 No |
Answer / harkamal singh
1)Distance between two earthing pit depending upon soil resistance.
2)Type of earthing
3)earth fault calculating.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / vel
As per IS3043:
Distance between plate earth electrodes shall be 8 m minimum.
Distance between pipe earth electrodes shall be 5 m minimum.
| Is This Answer Correct ? | 14 Yes | 19 No |
what is the difference between megger and earth resister ??
What is the ratio of Booster transformer?
what is the working principle of soft-starter & how it diff. from VFD ?????????
How many Zones can be in Conventional type fire alarm system & how can we detect the fire in Conv. type FAS?
Is there any Institution (Not AMIE)for giving B-Tech/M-tech in Electrical engineering for those who r in service? Give the details please.
Difference between HRG and NGR. Are they both the same thing
What are all present producing cost of Per KWH of various Fuel?
how can we Increase the Value Of Frequency in electric circuits
explain Xmer
How we can change the direction of rotation of Induction motor? Prove it using graphical methods.
Why current shoots up in the secondary on the knee point voltage during saturation test of CT? How core saturation effects the secondary current (while the primary side is open)? What the logic behind this?
Briefly define and explain the following different types of Pulse Amplitude Modulation (PAM) with some examples. i) 2-PAM ii) 4-PAM iii) 8-PAM iv) 16-PAM v) Quadrature Amplitude Modulation (QAM)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)