Hoe to calculate body earthing conductor size ?
Answer / aamod tripathi
The body earthing conductor sizing is done in india and
internationally by IEEE 80 :2000 standard and IS code 3043
These instruct the different formulae which are to be used
for calculation purpose generally it requires
1. fault current
2. time duration of the fault
3. a factor which is denoted by K and is dependent on the
material used for earthing.Table (1.D)(This takes into
account the ambient and operating temperature of the
material)
In case of a power house where many Transformers and the
switch gears are installed there we have to install
acompletee earthing grid which is like a square or
rectangular net of rods. the number of rods and ground rods.
The most important point in both the powerhouse earthing or
any other kind of earthing we have to keep in mind that the
earthing arrangement should have the resistance less than 1
ohm........ it is an essential conditon that must be
fulfilled.....
Is This Answer Correct ? | 14 Yes | 5 No |
what happens when the phase and earth wires comes in contact? and why
How can we calculate the rating of a transformer suppose if load is 1000KW?Formula?
when the rheostat kept in minimum to maximum position in motors what will happen?
what is the formula for calculating motor rating? Example: If we want to rotate a 1000 kg waight disc up to 100 RPM, which size motor will require?
what is auto transformer?
11. As per the theory current doesn’t flows in Neutral, but practically it is not applicable, explain why? 12. How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test? 13. Why the transmission lines are in 11kV, 22kV, 33kv, and why not 10kV, 20kV, 30kV? 14. Why do we generate 3 Phase AC Supply? It is possible to generate 4 Phase and 5 Phase explain it? 15. Explain why the Voltage drop will happen in 3 Phase line? 16. What is the equipment used to control the generator output? 17. What are the factors to be considered during the Synchronization? 18. What should be value of Circuit breaker operating time and tripping time? 19. Why the CT Secondary is rated as 5A generally? 20. At which time Synchronous generator act as a Synchronous Condenser?
how to calculate the bus-bar size. give formula with description
whats the application of voltage regulation? and whats the voltage regulation's device?
ro plant grundfos bm30type pump.we start the pump using siemens 3rw 4423-1bc44, 30kw soft starter. bur its failier frequently. so we planed to change the dol starter. sp please tell me any budy its possible or not翿შ†
How we can measure the thickness of bus bar for a given load ? any farmula Plz elaborate clearly.
why phase always came one direction in 5pin socket(right hand or left hand) which direction and why..........?
what is difference between vaccum circuit breaker and air circuit breaker?