Which ciass CT can be use in diff. protection. Can be use
5p20?
Answers were Sorted based on User's Feedback
Conventionally only PS class CT shall be used for unit
protections. But now a days, with the use of miro processor
based relays having facility of low impedance or biased
differential protection, 5P20 may be used as biasing in the
relay takes care of the unmatched characteristics of the
both side Cts.
Is This Answer Correct ? | 10 Yes | 0 No |
Answer / avdhesh
Class 5p20 CT is a protection class CT which is used for
normal protections. For differential protection you must
use class PS CT.
Is This Answer Correct ? | 13 Yes | 4 No |
Answer / persistence
yes 5P20 class CT can be used for differential
protection,In our industry they have been used for
transformer differential protection,transformer being 10 mva
and for bus differential protn. class PS has been used.
Is This Answer Correct ? | 10 Yes | 5 No |
Answer / dharmaraj
For diff.protn you must use ps(or) px class CT.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / dheena hitech
For diff protection we should be use PS or PX class Because
of yjat one ine is spl. class for diff and Dist protection
Is This Answer Correct ? | 1 Yes | 2 No |
The simple way of finding the leakage quantity and % in compressed air distribution system
how speed control of induction motor?
What is the transformenr turns ratio.
How to calculate the current carrying capacity of electrical cables
16 Answers Barqaab, Grasim, Havells, HM Cables, Janapriya, Polycab,
why transformer ratings are in kva
What is boost transformer in railway??
will three phase energy meter run without one phase
WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AND ITS CABLE IS 4CX50SQMM ,NOW ITS GETTING ABNORMAL HEATUP IN CABLE,PLZ TELL WHY ITS HEAT-UP?(CABLE LENGTH IS 15 METERS ONLY)
what are the accessories need to be added while doing estimation for the following: 1.MCCB 2.MCB 3.ACB
how much watts are equal to one unit of energy meter?
how much current capacity of 300 sq. mm cable (4 core aluminium) and 150 sq. mm cable ( 4 core aluminium)
what is over frequency protection