Which ciass CT can be use in diff. protection. Can be use
5p20?
Answers were Sorted based on User's Feedback
Conventionally only PS class CT shall be used for unit
protections. But now a days, with the use of miro processor
based relays having facility of low impedance or biased
differential protection, 5P20 may be used as biasing in the
relay takes care of the unmatched characteristics of the
both side Cts.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / avdhesh
Class 5p20 CT is a protection class CT which is used for
normal protections. For differential protection you must
use class PS CT.
| Is This Answer Correct ? | 13 Yes | 4 No |
Answer / persistence
yes 5P20 class CT can be used for differential
protection,In our industry they have been used for
transformer differential protection,transformer being 10 mva
and for bus differential protn. class PS has been used.
| Is This Answer Correct ? | 10 Yes | 5 No |
Answer / dharmaraj
For diff.protn you must use ps(or) px class CT.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / dheena hitech
For diff protection we should be use PS or PX class Because
of yjat one ine is spl. class for diff and Dist protection
| Is This Answer Correct ? | 1 Yes | 2 No |
WHAT IS VFD,FUNCTION, PURPOSE,
Your B.tech marks is being given in CGPA grade. How is it calculated?
which cable is used for 15 Hp monoblock pump 3phase and service wire Distance is 210 feet please tell me cable size Armaured
srij i need the relationship b/w KW AND KWH and with an electrical example. plz send if u can?
why are u join ntpc
What is transmission line potential gradiant?
hi Is there any possibilities to find out the rotation of a shaft or something else by using electromagnectic waves or by IR rays.If s then can v change the dir., of rotation of the same by remotely?& how? plz dn't any1 say "NO r CAN'T"
for selection of transformer we will considering 5 to 6 times of starting current of higher rating motor connected to secondary side. according to process wise we will start the motors gradually suppose if we will start 15 to 20 motors at a time wat will happen?
What will be the direction of rotation of a Alternator in case it goes in motoring action when connected with grid ?
sir pls tell me . our ct specifications are 120/5 ,2 core , 0.2 and 5p10 class , 30va and 30va buden. insted of 30 va i want use 15 va. can i use?
in 3 phase induction motor resistance value is how much
in 33/11kv stepdown transfomer, transformer will stepdown to 11kv & remaining 22kv where it will go..
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)