in transformers for ex. 100mva and 400kv the secondary
current is about 420 amps but for selection of bushing the
capacity of selected bushing is 2000A why there is such
big difference ?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The insulated leads of secondary from the Tr windings are
taken through hollow rods inside the bushing and connected
at the top.As the rod has to bear the all the mechanical
forces like torsion and strain, the wall has to be thick enough.
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / k.prakashchandra
I must have used the word 'pipe' instead of rod.Further,in
the condenser type bushing the oil inside is locked and
isolated from the oil in the tank.Hence it is deprived of
cooling. The pipe should be of much higher capacity to avoid
heating up due to the current flowing through it.
Is This Answer Correct ? | 0 Yes | 2 No |
When PRV operated at power transformer ,can anybody tell me particular pressure for 50mva transformer plzzz.
working of a diesel generator.
34 Answers ABC, AC, Cognizant, CTS, Directorate of Lighthouses and Lightships, KSL, Quippo, Shree Renuka Sugars, SRF, Svam Power, Tech Mahindra,
are there rmu for 3 transformer?
How to calculate Voltage regulation of 22 KV Over head Line.
how generator load test is conducted?what are the steps?
Dear sir, iam completed iti ncvt electrician 2000-2002 & diploma electrical eng completed 2008-2010 distance education in rvd university, still i got B licences only but my working company want C licences, how to i get c licencese pls reply me iam in critical situation thank you karthick 9841637803
state the disadvantages of carbon filament???
Hoe do calculate the Cable size for Amps rating ?
what is meant by twilight switches 7 where its applicable ?
what is the difference between elcb,rccb,mcb.
there is a power transformer 66/11kV in delta-delta connection has 5 feeder coming out from the secondary side. One of the feeder in it normally loaded (loaded than other feeder)and this feeder usually trips with double OCR causing the bank transformer to trip. Now if the load of this feeder is put on other transformer then that no problems occurs on that transformer or the load. However normally all the test(IR, PI, short ckt, open ckt,grounding test and other ) has been conducted for this but evertything transformer..... I am not geting what is the actual problem...
define superposition theorem thevnin theorem ,norton theorom?