whats the advandage of PMG in alternator?
Answers were Sorted based on User's Feedback
Answer / tareq harb
There are 3 types of excitation systems:
AREP, PMG & Self excitation.
in self excitation the AVR (Automatic Voltage Regulator)
takes its power directly from the out put terminals of the
generator, the main disadvantage of this method is that
when the generator output volatage drops the feeding to AVR
will be insufficient. suppose SHORT CKT fault takes place
on generator terminals as a result the output voltage will
drop too much & AVR shuts down directly with out feeding
this short CKT, if running on island mode (load sharing
mode) the hole system will trip.
But in PMG excitation system, PMG will feed AVR with the
same power nevertheless out put volatge, in case of short
ckt PMG alternator can supply 3 times its rated current for
10 seconds giving enough time for generator breaker to trip
eliminating the short ckt with out affecting the system.
as we see the main advange of PMG ALTERNATORS is its
enhanced immunity against short ckts.
Self excited systems is preferable in single mode operation
as it is cheaper & shorter prime movers.
PMG is strongly recommended in island mode operation.
Is This Answer Correct ? | 23 Yes | 0 No |
Answer / j.c.das
PMG or Permanent Magnet Generator are used in brushless
excitation system. It is advantageous from the maintenance
point of view. It doesn't employ carbon brushes as it does
not have a commutator and so no regular wear and tear as in
carbon brushes.
Is This Answer Correct ? | 21 Yes | 7 No |
what is an isolation transformer??? what is its purpose??? what happens if it is not used where it should be used?????
why transmission voltage is 230kv and not 220kv which is a multiple of 11
1 Answers Mettur Thermal Power Station, Siemens,
Explain Active power,reactive power,how its related to each other , & inductive ,capacitive.
why the starting torque is high in dc series motor..
How to set an overload in a motor?
What will happened if the neutral of secondary of Xformer ( Star point) Note it's above KVA rated Xformer
how many testing use in power transformer?tell equipment names?
Is it advisable to buy a plot for house construction near High Tension Power lines? If it so how much distance it should be away from power line? Iam residing at Chennai, Tamilnadu, India.
how many safety really of DG sets.
difference between servo motor and synchronous motor
we have two generators different capacity on 15 MW and other 6MW at 11 KV , 15 MW gen. bus short level current 40KA,and 6MW short level current 25KA,, length of cable 100MTR between 6 MW from 15MW gen. for bus coupling . kindly tell any one can we use both NGR OR one NGR from any GEN. BOTH NGR has diff. rating. Tariq pakistan
why the check zone and main zone are used for Busbar Protn. scheem?