Answer / shaikh
The current in the secondary side of a CT (Current Transformer) is induced by the current flowing in the primary circuit. If the current continues to flow in the primary circuit and the CT is left "Open Circuit" then dangerous voltages can build up and cause damage to equipment when reconnected or personal injury by electric shock.
Therefore, shorting the secondary terminals of the CT allows current to circulate taking flux with, thus reducing the building up of flux; the higher the flux the higher the emf (voltage) induced; E = Blv.
| Is This Answer Correct ? | 22 Yes | 1 No |
Answer / aamirali
Current Transformer (CT)is used for measurement, control and as a protection device. We make short ckt secondary of ct because we can measure the ratio and polarity of secondary side. if it isnt short cktd it will not operate under over current on secondary side.
| Is This Answer Correct ? | 2 Yes | 10 No |
What is ht lt switchgear.
3 Answers Bhel, HBL Power Systems,
WHAT IS THE DIFFERENCE B/W THREE POINT STARTER AND FOUR POINT STARTER
what is the meaning of DSL
transformer phasor diagram under load explain it?
how to compare with Relay settings for HT< panels, RMU panel, and PSS CSS transformer?? 1) Load amps, 2)Tripping time, 3) CT ratio, 4)Cable size 5) Transformer KVA rating 6) transformer full load amps
what will happen when excitation of a synchronous machine is suddenly reduce to zero when it is running at full load..??
what is the ckt diagram of a tubelight and is it the simplest ckt of electrical engineering and also the component?
What is transformation ratio what it describes?
How can we find the breaking capacity of a Load breaker switch (LBS) fed from 11 kv supply??ex:50KA, 26kA etc???detailed step vice answer pls.
how calculate gd2 of ht motors
4 Answers Hindustan Copper Limited, Kohler India,
Which ciass CT can be use in diff. protection. Can be use 5p20?
1 no. 22 kV feeder is taken from state electricity board. 350 MVA is the S.C. MVA. now i am feeding this feeder to HT Panel having 2 outgoings which further supply to 2 Transformers. Can you please suggest me the type & rating of cables are 3 of these cables same? or they are different? please help...............
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)