what is the order of mgnetiation current in a current
transformer of 1000A/1A ratio?
Answers were Sorted based on User's Feedback
Answer / anand suresh
as no load current is about 4-5%of full load current
magnetisation current would be less than that i.e 2-4%of
full current so maanetisation current would be around 2%of
1000 i.e, 20A
Is This Answer Correct ? | 2 Yes | 1 No |
how to conduct dc resistance test for rotor of an alternator and how to measure the rotor dc resistance value theoritically?
Show formula which gives full load current 4.8 amps of a 3 HP motor and 27 amps of a 20 HP motor having 3 phase 460 volts, 0.8 Pf.
I need to calculate the Battery bank back up for below configuration:- UPS - 120 KVA Battery Bank - 200Ah Volt of each cell - 12 V Total No of cell - 34 No's Can you please help me to get the battery back up time for above configuration...? along with formula
What is the use of oil in transformers?
how we can measure the dc current instead of clamp meter ?
What is the relationship between the sending end and receiving end?
Can any body describe me why a soft starter is used for 6.6kv induction motor instead of VFD ?
Please sent me some previous year question papers of BSNL-JTO telecom and RRB in ELectrical Engineering to varshashahi@yahoo.com
why shoud in High tension cable( above11KV etc.,)a semiconducting material coating will be there on insulation?
why using eleven's multiple for substations?
For a Potential Transformer(PT), the primary neutral terminal must be grounded before energization. Why....? What will be heppend if we energize the PT without grounded the primary neutral point? Why..........?
IF alternator SCR value will be high means what happen in alternator efficency at operating power factor of 0.8