TO operate transformers in parallel, vector symbol of the
both should be same.If one transformer name plate is not
there, how can we conclude that whether the transformer is
having the same vector symbol or not?
Answers were Sorted based on User's Feedback
Answer / guru
Check the vector group by carrying out VECTOR Group testing
( By Injecting a 3 Ph 440v or 230 V to the primary windings
and check the voltage between the terminals in secondary
side)
For each vector group there are standard values which has
to come in the secondary side
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rajendran
we can easily find out and confirm the vector group of the
transformer by using the standard test procedures.
| Is This Answer Correct ? | 3 Yes | 3 No |
This vector group test is done at site to check if their is
any damage in the windings during transportation and
erection.
3 -phase AC supply is given on HV side. R-Phase HV and r-
phase LV shorted.
Then to qualify the test following conditions are to be
satisfied after measurement of voltages.
nR+nY=RY, By>> Bb and Yb=Yy.
| Is This Answer Correct ? | 0 Yes | 0 No |
can we use ELCB and RCBO in one db
How many kw will suply from one db
what will happen at the time of CT saturation?and what will be the Relay's function at the time of CT saturation?
why we remove capacitor connection in 3 ph Induction Motor while taking noload test.
What are the applications of different multistage amplifiers?Plz also write advantages of these amplifiers? Thaaaaaaaaanx
why various test are performed on electrical panels & power cables before commissioning on site & what are these test???
What is effect of harmonic current (Draw by VFD) on power system/ electrical Equipments ?
i am electrical and elctronics engg passed out in 2009 want to attend for reliance placements.plz send me apttitude ,technical and hr question answers to my mail plz. my mail id-kat.bindas@gmail.com
1.stranded resistance values of motors? 2.how to calculate the resistance values of single phase and 3phase motors?
I need to connect a synchronous generator to the grid using automatic synchronization and two circuit breakers (one for synchronization, one for end connection to the grid), how to determinate the required diameter of the cables?
In a company the lines carrying 33KV but the load is below 10000Volts so we know that <11KV we can put 11KV lines but the lines are 33KV,..so how we can step down the voltage to 11KV with out erecting a substation
Can HT cable(11kv cable) be used for 415V, 700A requirement.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)