TO operate transformers in parallel, vector symbol of the
both should be same.If one transformer name plate is not
there, how can we conclude that whether the transformer is
having the same vector symbol or not?
Answers were Sorted based on User's Feedback
Answer / guru
Check the vector group by carrying out VECTOR Group testing
( By Injecting a 3 Ph 440v or 230 V to the primary windings
and check the voltage between the terminals in secondary
side)
For each vector group there are standard values which has
to come in the secondary side
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rajendran
we can easily find out and confirm the vector group of the
transformer by using the standard test procedures.
| Is This Answer Correct ? | 3 Yes | 3 No |
This vector group test is done at site to check if their is
any damage in the windings during transportation and
erection.
3 -phase AC supply is given on HV side. R-Phase HV and r-
phase LV shorted.
Then to qualify the test following conditions are to be
satisfied after measurement of voltages.
nR+nY=RY, By>> Bb and Yb=Yy.
| Is This Answer Correct ? | 0 Yes | 0 No |
374kvar capacitor bank connected across 600kw,6.6kv motor.what will happen if motor run at 50% , whether full kvar applied or half?
Can we loop AC neutral wire with DC neutral wire?
1. which type of transformer connection is preferred in case of power supply transformers? (A) Star/Star (B) Delta/Delta (C) Star/Delta (D) Zig Zag/Star 2. In a power transformer usuall which winding is closer to the core? (A) Primary winding (B) Secondary winding (C) Low Voltage winding (D) High Voltage winding 3. The power factor of a purely inductive load is (A) Zero (B) Lagging (C) Leading (D) Unity.
9 Answers CECRI_Central_Electrical_Research_Institute,
how to calculate the cable size depending on the transformer rating
How to calculate the cable size (XLPE)for suitable to 120KW load (if Motor or heaters etc)
The objective of connecting a resistance and capacitance across gate circuit is to protect the SCR against
what is mean by single phasing used for electrification in rural area of maharashtra ?
Whats meant by trivector meter where it is connected at the substation?
20 Answers GPIL, Infosys, Jakson, L&T, Secure Meters,
what is diffrent of RCCB & MCCB
Explain the term parallel path in dc machin ?
Why DG set rating in KVA
What is PQA???Applications........
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)