TO operate transformers in parallel, vector symbol of the
both should be same.If one transformer name plate is not
there, how can we conclude that whether the transformer is
having the same vector symbol or not?
Answers were Sorted based on User's Feedback
Answer / guru
Check the vector group by carrying out VECTOR Group testing
( By Injecting a 3 Ph 440v or 230 V to the primary windings
and check the voltage between the terminals in secondary
side)
For each vector group there are standard values which has
to come in the secondary side
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rajendran
we can easily find out and confirm the vector group of the
transformer by using the standard test procedures.
| Is This Answer Correct ? | 3 Yes | 3 No |
This vector group test is done at site to check if their is
any damage in the windings during transportation and
erection.
3 -phase AC supply is given on HV side. R-Phase HV and r-
phase LV shorted.
Then to qualify the test following conditions are to be
satisfied after measurement of voltages.
nR+nY=RY, By>> Bb and Yb=Yy.
| Is This Answer Correct ? | 0 Yes | 0 No |
why occ characteristics of generator is also called as magnatization characteristics ?
what are the current specifications of bus ducts ? i ve seen in IPBD bth 22000 A and 1500 A in 400 kv switchyard . why it is so??
why bucholtz relay placed inclined in transformer?
what is the excess air in furnace
What are the function of different components of servo motor?
What will be in Mahagenco Trade Test Exam? I want to know the same.
How to use a insulation resistance tester on a three phase electric motor?
How can transformer oil be used in transformers with voltage rating above its breakdown voltage?
How to arrange a hous hold earthing system to keep minimum earth resistance( below 7ohms).
draw vector diagram and +ve,zero sequence diagram of symmetrical three phase fault.
what is the purpose of fuse?
Why should The rating of 11 kV DO Fuse is in mulyiple of hundred(200 Amp. 40 Amp, etc) Ampere wheareses the its fuse elemnt has rating in just few Amp (< 12 Amp)? ( Is it jusy beacuse of factor of safty).
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)