If the load is 10Kw and power factor has to improve from 0.5
to 0.8,how can we select the capacitor rating
accordingly.Illustrate by showing formula?
Answers were Sorted based on User's Feedback
Answer / guest
at 0.5pf Apparent power is 10/0.5=20VA
reactive power = 17.321kVAR.
At 0.8pf
APPARENT POWER =10/0.8=12.5VA
Reactive power=7.5kVAR
So we need to provide (17.321-7.5)=9.821kVAR reactive power
through capacitor to bring of up 0.8 from 0.5.
So we need a capacitor rated for approximately 10kVAR to
achieve the target.
ANS= CAPACITOR RATING 9.821kVAR (approximately 10 kVAR)
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / prasad damodar bhoir
kvar= kw (tan phi 1- tan phi 2)
cos phi 1= 0.5, phi 1= cos inverse 0.5= 60
cos phi 2= 0.8, phi 2= cos inverse 0.8= 36.86
kvar= 10 (tan60 - tan 36.86)= 10 (1.73-0.74)
kvar= 9.9
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / h salim
Load = 10 kW
cos phi 1 = 0.5
cos phi 2 = 0.8
Rating of capacitor Qc = kW(tan phi 1- tan phi 2 )
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / prakash g.r.
Calculation of Required Kvar
Initial or Present Power Factor =Qi,
Required Power Factor = Qd
KVAr= KW(TANQi-TANQd)
Qi=COS-1PFi = Initial Power Factor Angle
Qd=COS-1PFd = Final Power Factor Angle
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ahatesham
at 0.5pf Apparent power is 10/0.5=20VA
reactive power = 17.321kVAR.
At 0.8pf
APPARENT POWER =10/0.8=12.5VA
Reactive power=7.5kVAR
So we need to provide (17.321-7.5)=9.821kVAR reactive power
through capacitor to bring of up 0.8 from 0.5.
So we need a capacitor rated for approximately 10kVAR to
achieve the target.
ANS= CAPACITOR RATING 9.821kVAR (approximately 10 kVAR)
| Is This Answer Correct ? | 2 Yes | 0 No |
Kvar = KW * [ tan (cos^-1* Current PF) - tan (cos^-1* Required PF)]
| Is This Answer Correct ? | 0 Yes | 0 No |
one electromagnet is called
I HAVE A INCOMING 100A MCCB TPN 25KA, CABLE LENGHT OF 80M 70MM CABLE SIZE FROM MAIN SUBBOARD TO NEW DB.BASE ON THE FAULT LEVEL SETTING OF 45KA.I WOULD LIKE TO FIND OUT 25KA ENOUGH KA. APPRECIATE IF SOMEBODY CAN ASSIST ME WITH FORMULA FOR THIS. FRM: JEFF
Can 60 Hz transformer be used inplace of 50 hz transfromer?
For DG or Transformer body earthing, is it necessary to terminate the earth bus to earth pit directly? If not terminated to earth pit directly in earth pit and connected to any common bus strip which ultimately connects to earth pit, what will be the pros and cons?
1) What are your personal strength? 2) What are your personal areas of improvement? 3) What are your expectations from from a particular job? 4) what are your carrier objectives?
Without seeing the nameplate descriptions of a rotating machine,Is it possible to say which one is a motor and which one is a generator? How would you certain this?
We have AC-transformer 110/13.8kv,40MVA.If DC-Voltage=110kv is applied in its primary what will happen?
hi if anybody got model questions for cpcl Grade'A' electrical engineer position.send it to my mail please krishkumar22@gmail.com
i have dry type transformers can you help me that how many tests i can do to know the performence of transformer and also please tell me about the BDV test and Insulation resistance test in oil cooled transformers
what is the defination of 'Mass' & 'Weight'
what is mean by unity power factor?why are u calling Resistivity load also unity power factor?
what is meant by transformer oil temparature
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)