How can we calculate the rating of capacitor bank to be
connected for a particular load(ex.100kw)to improve the
power factor from 0.8 to 0.9?
Answers were Sorted based on User's Feedback
The rating of capacitor bank is in kvar.Kvar rating can be
found out by power traingle.
active power=100kw
let the angles corresponding to power factors .8 and .9 be
A1 and A2 respectively
then reactive power required to improve the power factor
=100sin(A1)-100sin(A2)
| Is This Answer Correct ? | 18 Yes | 9 No |
Answer / mandeep singh
its.....kvar =capacitor bank 2 b installed,p=100kw,
kvar1=ptan(cosinverse 0.8),kvar2=ptan(cosinverse0.9)
kvar=kvar1-kvar2
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / ravikumar
kvar=kw(1.732) (TAN PHI1-TAN PHI2)
HERE PHI1=0.8
PHI2=0.9
THIS IS THE FORMULA REF; powersystems v.k. mehata
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / pasuvaraj
Mr Ravikumar, When your calculating the KVAr, you using the
KW in the Formula, How you consider the KW, The KW after
the KVAR Added or Before Added. This my doubt in your
formula you have explained
| Is This Answer Correct ? | 3 Yes | 4 No |
To measure insulation resistance of 11KV cable between core & armour, what should be the test voltage & duration?
an ac induction motor gets overheated when operated at a low frequency of 25 hz a instead of 50 hz. reason?
Pls explan the OLR setting in VCB at HT yard
EXPLAIN THE TERMS "INTEREST AND DEPRECIATION" AS APPLIED TO ECONOMICS OF POWER GENERATION.
What is expand formation of AYFY cable
What do you mean by passive circuit elements and why these are called passive?
What will be the voltage impact on secondary side of two transformers with different vector groups when both voltages are compared.
what is the working principle of three point starter of dc motor?
1 Answers Ashok Leyland, Cap Gemini, Infosys, Just Dial,
which on of the transformer have more core losses and why? 1. Distribution Transformer 2. Power Transformer
what is ideal insulator. what are its parameter. Is poecelain insulator comes under this category.
Dear sir, my knowledge about cable size determination is limited. Though I read examples I could not calculate the Cable size required for electric driven pump 40 KW, 380 Volt, 50 HZ, 50 meter from transformer and it is three phase star delta starting. Please help as there is no one in my surroundings to help.
No load efficiency of transformer is ___________ than full load efficiency
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)