How can we calculate the rating of capacitor bank to be
connected for a particular load(ex.100kw)to improve the
power factor from 0.8 to 0.9?
Answers were Sorted based on User's Feedback
The rating of capacitor bank is in kvar.Kvar rating can be
found out by power traingle.
active power=100kw
let the angles corresponding to power factors .8 and .9 be
A1 and A2 respectively
then reactive power required to improve the power factor
=100sin(A1)-100sin(A2)
| Is This Answer Correct ? | 18 Yes | 9 No |
Answer / mandeep singh
its.....kvar =capacitor bank 2 b installed,p=100kw,
kvar1=ptan(cosinverse 0.8),kvar2=ptan(cosinverse0.9)
kvar=kvar1-kvar2
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / ravikumar
kvar=kw(1.732) (TAN PHI1-TAN PHI2)
HERE PHI1=0.8
PHI2=0.9
THIS IS THE FORMULA REF; powersystems v.k. mehata
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / pasuvaraj
Mr Ravikumar, When your calculating the KVAr, you using the
KW in the Formula, How you consider the KW, The KW after
the KVAR Added or Before Added. This my doubt in your
formula you have explained
| Is This Answer Correct ? | 3 Yes | 4 No |
does the Trivector Meter of three phase automatically takes care of the low power factor and gives the reading accordigly or it does not take care of the Power factor while giving the readings please explain
15hp motor wound by 0.9mm & 0.95mm magnet wire. at no load test it draw 4.2A current. Another motor with same condition draw 9.2A current. How can that occur? pls help
What is the distance between each insulator in 33kv transformer and how can it calculate
List out the the types of Mounting Light fixture?
i have installed my solar site of 6.7kw and is working perfectly , can somebody tell me that how can i measure my solar irradiation kw/day/sq m ?
In case of dc circuit Whether dc current will pass through capacitor after it gets charged?
Define closed loop control system.
Hi all I had applied for the RRB test in the ELECRICAL category. I would be pleased if any of you can sent me previous year question papers. Please forward the question papers to varshashahi@yahoo.com Thanks and regards Varsha
Any one can explain if there is any harm from humming noise heard from air circuit breaker : we have 415 switch board having two incomers from transformers 3.3KV/415V , when bus coupler closed, and open one ACB incomer to work in one of the transformers, the current started hunting around 50 Amps, and heard humming noise from the air circuit breaker, although the load current was only 1200 amps while the ACB capacity is 2500 Amps, and the transformer 1600 KVA. The same didn't happen when taken the other transformer offline. Why this humming noise and current fluctuation? is there any implication or danger, bearing in mind that we just returned everything back to normal and stopped the maintenance of the transformer. Shall we go ahead and ignore this noise?
We have two 1 phase heating coils having same resistance of 25ohm, but during operation one takes 3A and other 6A Is it posiible Pls. explain
1.what is the reason for transformer and lightning arrester blast in 33kv system
WHY CFL can't made in shape of bulb.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)