Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


what is the difference in MCB, MCCB, RCCB, ELCB, & MPCB
(motor protection circuit bracker)

Answers were Sorted based on User's Feedback



what is the difference in MCB, MCCB, RCCB, ELCB, & MPCB (motor protection circuit bracker)..

Answer / sukhvinder

mcb : miniature circiut breaker.
mccb : metal clad or moulded case circuit breaker.
rccb : residual current circuit braeker.
elcb : earth leakage circuit breaker.
mpcb : motor protection circuit breaker.

Is This Answer Correct ?    689 Yes 63 No

what is the difference in MCB, MCCB, RCCB, ELCB, & MPCB (motor protection circuit bracker)..

Answer / prajapati

MCB - Miniature Circuit breaker, is having overload and
s.c. protection & used in domestic application

MCCB - Moulded case Circuit breaker, is having overload and
s.c. protection & used in Industrial application & Having
high s.c. capacity

RCCB : Residual current operated circuit breaker, is used
for protection against electric shock

ELCB : Earth leakage circuit breaker & is same as RCCB

MPCB : Motor protection circuit breaker, is used for
protection of motor, having s.c. and overload protection
more effective to protect motor

Is This Answer Correct ?    581 Yes 50 No

what is the difference in MCB, MCCB, RCCB, ELCB, & MPCB (motor protection circuit bracker)..

Answer / nn duc

Prajapati's answer is good.

ELCB is actually voltage operated and need a stable
connection to earth electrode.

RCCB is actually seeing the difference in the current
flowing in and out of the circuit. If there is a leakage,
the sensing circuit will detect the leakage and trigger the
RCCB to trip.

Is This Answer Correct ?    150 Yes 21 No

what is the difference in MCB, MCCB, RCCB, ELCB, & MPCB (motor protection circuit bracker)..

Answer / pradeep

If RCCB is same as ELCB, can we use ELCB where RCCB is
specified.

Is This Answer Correct ?    136 Yes 59 No

what is the difference in MCB, MCCB, RCCB, ELCB, & MPCB (motor protection circuit bracker)..

Answer / prit

mpcb has an inbuilt contactor and relay.so need for
external contaectors and relays. mccb ther is no contactor
and relays, we have to provide.


MCB (Miniature Circuit Breaker)-rated current not more than
100 A. Trip characteristics normally not adjustable.
Thermal or thermal-magnetic operation. Breakers illustrated
above are in this



An Earth Leakage Circuit Breaker was the first name given
to what is now called a Ground Fault Circuit Interrupter
(GFCI) . The original type of ELCB or GFCI was designed
only to detect a current flowing in the safety "ground"
or "earth" wire.


A Miniature Circuit Breaker. An MCB is a device designed to
protect a circuit's wiring from the serious damage which
would be caused if it has to carry a current which is too
high for the diameter of its wires. Such a current could
easily heat up the wires so much that their insulation
melts. If that situation were allowed to develop further it
would soon cause the wires in a cable to short out and to
burn so hot that they could easily cause a house fire.

Is This Answer Correct ?    70 Yes 14 No

what is the difference in MCB, MCCB, RCCB, ELCB, & MPCB (motor protection circuit bracker)..

Answer / souvik ghoshal

Mcb: miniature circuit breaker comes with max. 100A/10kA
rating earlier but but now it is available for 125A/16kA
rating. Based on thermal mechanism breaks the circuit under
short circuit condition.
Mccb: moulded case circuit breaker comes with upto
1000A/25kA rating. Based on thermal mechanism for overload
protection of load and magnetic mechanism for instant
tripping during short circuit.
Rccb: residual current circuit breaker, basically a kind of
ELCB which determines the difference between line and
neutral current,whenever it crosses the set value it trips.
Normally used in 3 phases while its single phase version is
known as RCD.
ELCB: earth leakage circuit breaker, basically used in DB
incomer is of two types, current operated and voltage
operated. In case of voltage operated one,the difference of
potential is measured between grounded spikes and terminal,
while in case of current operated one, you can call this a
RCCB.
MPCB: motor protection circuit breaker consist of separate
contactors used for protecting motors under over current
condition,which is generally caused due mechanical issues
of motors.

Is This Answer Correct ?    52 Yes 10 No

what is the difference in MCB, MCCB, RCCB, ELCB, & MPCB (motor protection circuit bracker)..

Answer / suresh

MCB - Miniature Circuit breaker, is having overload and
s.c. protection & used in domestic application

MCCB - Moulded case Circuit breaker, is having overload and
s.c. protection & used in Industrial application & Having
high s.c. capacity

RCCB : Residual current operated circuit breaker, is used
for protection against electric shock

ELCB : Earth leakage circuit breaker & is same as RCCB

MPCB : Motor protection circuit breaker, is used for
protection of motor, having s.c. and overload protection
more effective to protect motor

Is This Answer Correct ?    35 Yes 7 No

what is the difference in MCB, MCCB, RCCB, ELCB, & MPCB (motor protection circuit bracker)..

Answer / ashok

MCCB and MCB is for over load protection and Earth Fault protection.MCCB is for heavy duty ie it with stand more fault current.
RCCB is only for Earth leakage protection

ELCB will protect Overload, short circuit,Earth leakage and used where the fault current is more

Is This Answer Correct ?    43 Yes 24 No

what is the difference in MCB, MCCB, RCCB, ELCB, & MPCB (motor protection circuit bracker)..

Answer / prawin

example phase wire is going on the tube light.if that phase wire touch in earth mccb will trip automatically.

Is This Answer Correct ?    42 Yes 27 No

what is the difference in MCB, MCCB, RCCB, ELCB, & MPCB (motor protection circuit bracker)..

Answer / rajesh achuthan nair kumaramka

mcb Miniature circutebraker will protect a circuit's wiring
from the serious damage which
would be caused if it has to carry a current which is too
high for the diameter of its wires. Such a current could
easily heat up the wires so much that their insulation
melts. If that situation were allowed to develop further it
would soon cause the wires in a cable to short out and to
burn so hot that they could easily cause braker is for
protect over load
An Earth Leakage Circuit Breaker was the first name given
to what is now called a Ground Fault Circuit Interrupter
(GFCI) . The original type of ELCB or GFCI was designed
only to detect a current flowing in the safety "ground"
or "earth" wire.
rccb (recidential current circute braker function is same
elcb

Is This Answer Correct ?    20 Yes 8 No

Post New Answer

More Electrical Engineering Interview Questions

What is basic impulse insulation level? And how it is calculated for sub- station?

2 Answers  


what is B , c & d curves in MCB characteristics i e Full Form of B , C & D . sir please give me answer

1 Answers   NCC,


Megger type of instrument is used to check??

8 Answers  


how we can calculate power factor without knowing current in 230v 100w load ?

10 Answers  


What is the effect of positive feedback on the stability of the systems?

0 Answers  


What are factors to be considered while we selecting the Core Balance Current Transformer for Earth fault protection

0 Answers  


what is the formula for converting dc power(watt) to ac power (watt)?

3 Answers   ABB,


detailed procedure how we calculate cost for pcc m10 and rcc m20 including centering and labour excluding steel/ iron

0 Answers  


WHICH TYPE OF TRANSFORMER IS USED IN POWER TRANSMISSION BASED ON TRANSFORMER CONNECTION ON PRIMARY AND SECONDARY SIDE

3 Answers  


How to see the inductance in a transmission lines

0 Answers  


how can we use isolator as breaker

4 Answers  


Whag is the PS class of accuracy of CT?

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)