what is the difference in MCB, MCCB, RCCB, ELCB, & MPCB
(motor protection circuit bracker)
Answer Posted / nn duc
Prajapati's answer is good.
ELCB is actually voltage operated and need a stable
connection to earth electrode.
RCCB is actually seeing the difference in the current
flowing in and out of the circuit. If there is a leakage,
the sensing circuit will detect the leakage and trigger the
RCCB to trip.
| Is This Answer Correct ? | 150 Yes | 21 No |
Post New Answer View All Answers
Mention the disadvantages of low power factor? How can it be improved?
Name of the relay of low lub oil presuure in DG sets
What is the numerical quantity of sqcm?
sir i had plane to do some project with the base of hopkinson test in AC supply its possible
what is vA rating and class of a ct.
I have 2500KVA transformer delta/star,13.8KV/380V provided with LV 4000A breaker. Already I have 2300KW motor feeder with a full load 90%. Is it possible to connect another 1600A from that breaker? If so how the calculation is done?
Explain the terms real power, apparent power and reactive power for ac circuits and also the units used.
What happened ,If 3 phase clearance not maintained in 33KV Line,11KV LIne etc?
What is the relationship between voltage,current & frequency?
what is the use of expulsition protective gap in 11Kv line.
For a three phase induction motor, what will be the effect on motor if the neutral of the system is shifted to say 20 deg.?
Dear sir, I completed DECE In the year 1995.Now i am working in a private company from last 10 years as an Electrical supervisor.The company having a 1000 KVA transformer.Now i try to apply "C" Licence. I am eligible or not.If not eligible,pls give solution.
why tertiary winding is used in transformer with diagram?
State and define ohm’s law?
specific difference of ICT&Auto Transformer