what is the difference in MCB, MCCB, RCCB, ELCB, & MPCB
(motor protection circuit bracker)
Answer Posted / nn duc
Prajapati's answer is good.
ELCB is actually voltage operated and need a stable
connection to earth electrode.
RCCB is actually seeing the difference in the current
flowing in and out of the circuit. If there is a leakage,
the sensing circuit will detect the leakage and trigger the
RCCB to trip.
| Is This Answer Correct ? | 150 Yes | 21 No |
Post New Answer View All Answers
how can i find cable size from current rating?
Type of motor stater detail and working detail
please send me privious exam's queation papers of section engineer(electrical).
Is neutral transformer can be called as control transformer?
what is the solution for meger test failed the MV cable?
How can calculate the rating of a alternator for a given specific load with formula
which protection function should measure RMS value of current&DFT value of current?
what is the min and max ohmic resistance for the earthing rod installed for lighting poles for street light network
In constant power region of 3-phase IM torque-speed characteristics, if frequency increases slip A does not alter B decreases C increases D none of above
surge tank, hrc fuse, earthing transformer, firm power objective type
how we can calculate the efficiency of a diesel generator ?
WHY CBCT USE ONLY IN Y PHASE NOT OTHER PHASES
How to calculate fault level of 11 KV system
A 400KVA transformer has 400 Hz frequency. If the frequency is changed to 50 Hz, then what will be the new KVA rating?
What are the specifications for getting approval of Substation?