what is the type of winding connection( star or delta) in
1HP to 5HP motors. How to check the motor winding
connections( star or delta) if not provided in the
nameplate?
Answers were Sorted based on User's Feedback
Answer / a.lingadurai
The winding resistace varies according to the connection
of star / delta. When star connected motor, measured
resistance shows the value of two resitance in series.
When delta connected motor,measured resistance shows the
value of two resistance series and another resistace
parallel with them. So we can identify by the value of
resitance.
Also the phase current of motor is equal to line current
for star connected motor. For delta connected motor the
line current is 1.732 times of phase current.
| Is This Answer Correct ? | 25 Yes | 4 No |
Answer / karl
Most nameplates wont say whether to connect in Delta or
Star but will show a Delta symbol or star symbol with a
voltage rating of current rating next to them. Sometimes a
symbol not even shown but 2 levels or voltage and currents.
This is because this gives you 2 choices of voltages to
connect to. Example if you have a 415V three phase supply
and your motor nameplate shows 230V Delta and 400V Star you
should connect the motor in Star. If it just shows 400V
this usually means you connect it in Delta. If you
connected this motor in Star it would not give you full
output power. These motors sometimes use a star, delta
starter which when in star runs at lower start current.
| Is This Answer Correct ? | 16 Yes | 3 No |
Answer / pillay
I agree with only KARL.If the connection is not mentioned in
the name plate than it is anybodies guess wish you best of luck.
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / naganath jamadar
All 3 phase motor are winding with RYB 3 saperate coils winding started point and finished point so totale six connection you can do it easy star or delta using links in terminal s
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shri..
As per my knowledge in star connections only three leads
are coming at terminal box.
And in star delta winding six leads are coming in terminal
box.
In star connection DOL starter are using.
In star delta starters
When pressing on button of starter the starter make star
connection after releasing the button starter makes delta
connection.
| Is This Answer Correct ? | 21 Yes | 25 No |
How to calculate the no of Ceiling fan (1200mm sweep) per unit area?
hi how are you? i m in walchand college of engg. do you have interest in join me through email so send your email id
What happen if ac supply is fed to rotor of the alternator?
On what basis primary and secondary of a transformer is chosen?
What is an infinite bus bar?
am commissioning the trafo without connecting the neutral therefore unbalance will occur what is the alternative solution for this?
What is the use of core in the transformer?
How to calculate the cross section area for a 350 m cable, motor power is 26 kw???
How would you supply power to a village which is very far from a sub-station and has only a 11kV line running near by?
The SFC of an engine is 0.25 kg/kW hr. when the fuel used has a calorific value of 36000 kJ/kg. the thermal efficiency of the engine is
how the earhing is done on ship and airplane.
what is the diff of mcb and mccb
2 Answers NSN, Sterling Wilson,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)