how to calculate the powerfactor in induction motor having
name plate details? for example 1 h.p motor 1.86 A 415 V
Answers were Sorted based on User's Feedback
We know P=VICOSф.
Here, P=1H.P=746W,V=415v,I=1.85amp
Now putting this value on the equation simply we get the PF.
746=415*1.85*COSф
746
=>COSф=----------=0.9716 and it must be lagging.
415*1.85
More info: Earn and Learn pls visit
http://a2zengineering.blogspot.com/
Is This Answer Correct ? | 18 Yes | 2 No |
Dear Zakir husan
What is 1092 in your equation .
That we know that
p=root3 v*i*cos phi
1 h.p =746 watts = 1.732*415*1.86*cos phi
cos phi= 746/1.732*415*1.86
= 0.55 and pf leging.
Is This Answer Correct ? | 12 Yes | 3 No |
Answer / aaaa
its depend on phase no of the motor.(3-phase , single phase)
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / vishnu
here P=1H.P=746w,
I=1.86,
V=415V
FORMULA P=1.732*V*I*COS phi
cos phi=746/1.732*415*1.86
cos phi=0.55
Is This Answer Correct ? | 9 Yes | 5 No |
Answer / jagjeet
Dear Satish
The power factor dependent on the loading factor of the
induction motor , You can measure the Line current and apply
the formula suggested by Zakir or you can refer the
characteristics charts of Motor to find out the Power Factor.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / shakus
@Sakthish_kumaar
Please mention whether the motor is single phase or three
phase?
apply for single phase>>
P=VIcosØ
and Apply for three phase>>
P=√3VIcosØ
Is This Answer Correct ? | 2 Yes | 0 No |
how can i get the formula to find out the cable size if i know the load of main fuse protection.
difference b/w current and voltage relay?
Why lightning arrester blast in rainy day?
1 Answers Eco Cement, Mahaveer, MBDL,
what is RNG in the DG synchronizing by PLC?
why generator is star connected ?
what is slip?
th how could we differentiate between armoured copper and armoured aluminium cable what is the basic application? why we prefer the armoured copper as compared to armoured aluminium.
why we test the core balance of the transformer?
What is the Full form of Rccb,MCCB,
11 Answers Marriott, Maruti Suzuki, MCB, PCC, RCCB, Torrent Pharma,
3 ph motor connected in star delta starter. when we start the motor it run in star but when in is going in delta it trips the main incoming supply. why?
Whats changes in Transformer Oil BDV in changes in temp or Climate?
explain the operating principles of CVT & RVT