Can HT cable(11kv cable) be used for 415V, 700A requirement.
Answers were Sorted based on User's Feedback
Answer / ashish baluni
Cable used for HT is designed for High Voltage and low
current carrying capacity. But for Low voltage rating
current requirment is very high which would cause Excess
heating in cable and will result in Puncturing of cable at
weak point.
For Ex- HT side Power=HT Vol* HT Current,if this cable
would be used for Low voltage then Power will be same. Thus
LT Power= HT Power
> 415*700 = 11000* I (Power factor is assumed to be unity)
> I= 26.5 Amp (For HT cable)
Thus,HT cable cant be used for Low voltage at High Current.
| Is This Answer Correct ? | 16 Yes | 1 No |
Answer / v.senthilkumar
We can use HT cable for 415V, 700A. But you have not
mentioned any HT cable rating. If you mention HT cable
rating then we can analise whether it can be use or not.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / ranjit
Actually we cant use HT cables on 415 V LV side because of
without neutral cable. we can use HT cable with neutral
additionally. Neutral cable based on copper size which is
inside on HT cable. Because normally HT cable insulation
more less copper. because HT side High voltage less
current. But economic wise this is not good idea also.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mehul
we can't use h.t. cabel as l.t. cable.
because the cost of your h.t. cable is much higher han same
rating h.t. cable.
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / mathew
normally, for HT we are using 240Sqmm cable in ring circuit. this 240sqmm cable is not sufficient for 700A, 2x240sqmm is sufficient for 700A. but we can use this 240 for both 11KV and 415V, thats not a problem.
| Is This Answer Correct ? | 2 Yes | 5 No |
what is the difference between vector scale and vector diagram?
if the 10 hp motor name plate indicates rated current as 13.6 amp the what will be the thermal relay setting? Why? And in how much time relay will trip at the set value?
How can eliminate noise problem inside temperature controller temp. variation due to contactor chattering problem.
How amny AH battery required for 600va inverter ?And how many hours it will give backup for ceiling fan ?
what is brushless generator?
why it is necessary to maintain frequency constant in a power grid ?
WHAT IS THE ROLE OF ELECTRICAL & ELECTRONICS ENGINEER IN TCS.
What is the Power factor of DC Power system ?
number of I/O devices in siemense plc
can i use 10 mfd + 6 mfd instead of 15 mfd capacitor in single phase motor as running capacitor
Why the moulded plug comes with domestic appliances instead of assembled plug like anchor, Vinay 5/15 A.
what is the procedure to carry out BDV test of a transformer ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)