what is the diffrantial relay???????why we use it on the MDB
Answers were Sorted based on User's Feedback
Answer / afrooz
Differential relay is a current sensing zone protection
relay.It is used to protect alternators,transformers from
internal short ckt,internal earth faults.
| Is This Answer Correct ? | 7 Yes | 0 No |
DIFFERENTIAL RELAY is used to sense generator supply in two
different locations. in generator out put leads are six. in
three phase winding- three leads of begining of coils and
three leads of ends of coils.three leads are named R,Y,B
and other three leads are R1,Y1,B1. we make star connetion
by joint R1,Y1,B1 and make neutral point by this
junction.we ground this neutral.we provide three CT'S in
RYB side and three CT'S in R1 Y1 B1 side.
if any fault occurs in winding between RYB and R1 Y1 B1 the
resultant supply operates the differential relay and the
generator stops automatically.
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / gova
Diff relay compares the input current and output
current that flows through the equipment and if there is
any difference between them,then the relay will sense the
difference of two currents (called differential current)
and trip the equipment protected if the differential
current exceeds the setting.
diff relay used in transformer,Generator,lines,motors etc.
what is MDB.pl abbreviate it.
regards
gova
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / gova
Diff relay will trip not only for earth fault but for phase
fault occurring inside the transformer.
Diff relay should not operate for through faults or
external faults-(out zone fault,i.e beyond protected zone)
regards
gova
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pinaky
the above guy is 100 percent rite.
i can prove the matter how to calculate for differential relays
but am not a member rite now if u guys think that i can
share my knowledge with u please ask me to join Ur world.
regards
pinaky
by the way its called differential protection relay
make
seamens
abb
and few reputed companies with their proper logic settings.
Its a tough job to calculate the ct ratios for ct of ht and
lt protections.
ok enough for now
please remember me and i shall be ur friend for ever.
| Is This Answer Correct ? | 1 Yes | 2 No |
what is difference between delta-delta,delta-star transformers ???
why can't we provide dc supply to a transformer?
Which factor decide the colour of the light emitted from a Led?
what is the permissible bend in the LT& HT CABLES.
What must the distance between two MV cables be when they are laid on tray?
Why syn. Generators are used for the production of electricity?
calculation of knee point voltage of current transformer?
how does capacitor oppose sudden chane in voltage? how does inductor oppose sudden change in current?
4 Answers AAA, Iqra University,
1 sq mm conductor=? how many amps
what is diffrential relay used in generator plz give brief explanation
The armature of shunt dc motor has 0.8ohm resistance and motor is to run on 120V circuit.If motor is suddenly thrown on circuit while armature at standstill then current drawn by motor will be??Also back emf in normal running is 110V
Myself completed B.Tech ECE in private university but i am working as an testing and commissioning engineer in electrical field whether i am eligibility to apply electrical licence.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)