Why the capacitor are connected in Delta(Three Phase) for
power factor improvement ?
Answers were Sorted based on User's Feedback
Answer / ankamsreekar
The effective capacitance is 3 time more in delta as
compared with star connection provided that same capacitors
are used.
| Is This Answer Correct ? | 19 Yes | 5 No |
Answer / sreenu
Becasue, in delta connection,voltage of three phases is
equal and the power factor( Reactive power)is depends on
voltage.
If you use star connected capacitors, the voltage may vary
due to unbalenced loading of capacitor whcih is indirectly
depends on load.
| Is This Answer Correct ? | 13 Yes | 5 No |
Answer / dr. shahid
In delta the effect is 3 times as compared to when they are star connected.
Regards
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / jonathan r. lambert
Capacitors are paralleled with inductive (magnetic) loads
in delta, wye (aka "Star") and single phase AC power
sources to correct power factors so that motors,
transformers and other inductive loads appear to be
resistive. Power factor correction is a process that
cancels reactive current vectors leaving only a resistive
current. Inductive loads pull currents that contain both
resistive and reactive vectors. In power factor correction,
a capacitor's reactive current is used to cancel the
inductive reactive current created by magnetic coils in
inductive devices. If the capacitor is sized correctly the
current drawn by the capacitor will precisely cancel the
inductive magnetization current pulled by an inductive
load. The resulting motor current "seen" by the AC voltage
source will then be only resistive. Since power companies
charge for both reactive and resistive current, and since
only the resistive current is required to provide
horsepower and perform work, power factor correction
reduces the current drawn by inductive loads which reduces
the electrical operating expense. Hard to believe that
applying an additional parallel load, a capacitor, will
result in less total current but it works due to the
capacitive reactive current leading at +90 degrees and the
inductive reactive current lagging at -90 degrees, the two
parallel currents sum at the voltage source to equal zero
degrees and if the cap is sized correctly, zero amplitude.
| Is This Answer Correct ? | 3 Yes | 13 No |
CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE IT AS STEP UP TRANSFORMER BY GIVING 200V IN SECONDARY AND TAKING OUTPUT FROM PRIMARY?
On a transformer name plate %IZ(%Impedence) is mentioned. What is the meaning of %IZ and how it is calculated?
3 Answers Ambe Consultancy, Siemens,
what is the use of surge suppresser in 33 KV incoming panel. where it must be installed,inseries with incoming cable surge suppresser must be at incoming of the breaker are outgoing of the breaker
What is the effect of positive feedback on the stability of the systems?
Type of cable insulation?
How much pf maintan in dg set in 6o% load,when Dg runnig Neutaal Earthing removed what happen.
two 100W/230V bulb are connected in series. what would be the voltage drop across 1 bulb
What is transformer saturation?
what is the operation of UPS ? can any one answer me?
what is the different between bus section and bus coupler
Why the transformer rating is denoted in VA rating why not in KW
Why 66KV is step down to 11KV and then 433v, not directly 66KV to 433v ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)