Why the capacitor are connected in Delta(Three Phase) for
power factor improvement ?
Answers were Sorted based on User's Feedback
Answer / ankamsreekar
The effective capacitance is 3 time more in delta as
compared with star connection provided that same capacitors
are used.
| Is This Answer Correct ? | 19 Yes | 5 No |
Answer / sreenu
Becasue, in delta connection,voltage of three phases is
equal and the power factor( Reactive power)is depends on
voltage.
If you use star connected capacitors, the voltage may vary
due to unbalenced loading of capacitor whcih is indirectly
depends on load.
| Is This Answer Correct ? | 13 Yes | 5 No |
Answer / dr. shahid
In delta the effect is 3 times as compared to when they are star connected.
Regards
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / jonathan r. lambert
Capacitors are paralleled with inductive (magnetic) loads
in delta, wye (aka "Star") and single phase AC power
sources to correct power factors so that motors,
transformers and other inductive loads appear to be
resistive. Power factor correction is a process that
cancels reactive current vectors leaving only a resistive
current. Inductive loads pull currents that contain both
resistive and reactive vectors. In power factor correction,
a capacitor's reactive current is used to cancel the
inductive reactive current created by magnetic coils in
inductive devices. If the capacitor is sized correctly the
current drawn by the capacitor will precisely cancel the
inductive magnetization current pulled by an inductive
load. The resulting motor current "seen" by the AC voltage
source will then be only resistive. Since power companies
charge for both reactive and resistive current, and since
only the resistive current is required to provide
horsepower and perform work, power factor correction
reduces the current drawn by inductive loads which reduces
the electrical operating expense. Hard to believe that
applying an additional parallel load, a capacitor, will
result in less total current but it works due to the
capacitive reactive current leading at +90 degrees and the
inductive reactive current lagging at -90 degrees, the two
parallel currents sum at the voltage source to equal zero
degrees and if the cap is sized correctly, zero amplitude.
| Is This Answer Correct ? | 3 Yes | 13 No |
a transformer can have zero voltage regulation a)o pf b)1 pf c)lagg pf d)lead pf
at high temperature conductivity increases for conductor what will happen for long transmission when temperature is high?
what bridge circuit is used in Tandelta circuit
what is tpmo switch
Why is transformer connect parallel? why not series? ....plz...
the parts of transformers ?
1 Answers Bhel, Facility management,
how can I check HT cable ?
Is it mandatory statutory requirement of transformer oil filtration annualy despite oil is withstanding required dieelectrical strenth and all others parameters
what are the installation procedure of high voltage power transformer,CT,CB&PT?
is it true there's a big difference in using Cummins or Denyo...especially power output or leakage
Explain advantages of storage batteries
1 amp means-how many electron flow per second. ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)