Why the capacitor are connected in Delta(Three Phase) for
power factor improvement ?

Answers were Sorted based on User's Feedback



Why the capacitor are connected in Delta(Three Phase) for power factor improvement ?..

Answer / ankamsreekar

The effective capacitance is 3 time more in delta as
compared with star connection provided that same capacitors
are used.

Is This Answer Correct ?    19 Yes 5 No

Why the capacitor are connected in Delta(Three Phase) for power factor improvement ?..

Answer / sreenu

Becasue, in delta connection,voltage of three phases is
equal and the power factor( Reactive power)is depends on
voltage.

If you use star connected capacitors, the voltage may vary
due to unbalenced loading of capacitor whcih is indirectly
depends on load.

Is This Answer Correct ?    13 Yes 5 No

Why the capacitor are connected in Delta(Three Phase) for power factor improvement ?..

Answer / dr. shahid

In delta the effect is 3 times as compared to when they are star connected.

Regards

Is This Answer Correct ?    3 Yes 3 No

Why the capacitor are connected in Delta(Three Phase) for power factor improvement ?..

Answer / nsreekanth

To avoid circulating currents

Is This Answer Correct ?    1 Yes 7 No

Why the capacitor are connected in Delta(Three Phase) for power factor improvement ?..

Answer / jonathan r. lambert

Capacitors are paralleled with inductive (magnetic) loads
in delta, wye (aka "Star") and single phase AC power
sources to correct power factors so that motors,
transformers and other inductive loads appear to be
resistive. Power factor correction is a process that
cancels reactive current vectors leaving only a resistive
current. Inductive loads pull currents that contain both
resistive and reactive vectors. In power factor correction,
a capacitor's reactive current is used to cancel the
inductive reactive current created by magnetic coils in
inductive devices. If the capacitor is sized correctly the
current drawn by the capacitor will precisely cancel the
inductive magnetization current pulled by an inductive
load. The resulting motor current "seen" by the AC voltage
source will then be only resistive. Since power companies
charge for both reactive and resistive current, and since
only the resistive current is required to provide
horsepower and perform work, power factor correction
reduces the current drawn by inductive loads which reduces
the electrical operating expense. Hard to believe that
applying an additional parallel load, a capacitor, will
result in less total current but it works due to the
capacitive reactive current leading at +90 degrees and the
inductive reactive current lagging at -90 degrees, the two
parallel currents sum at the voltage source to equal zero
degrees and if the cap is sized correctly, zero amplitude.


Is This Answer Correct ?    3 Yes 13 No

Post New Answer

More Electrical Engineering Interview Questions

Why is it prefer to initiate circuit breaker failure by "86" lockout relay not by "94" tripping relay ?!

0 Answers   OEG,


what are the insulation properties.

2 Answers   Cable Wireless, MAHINDRA,


As all us know that the capacitor panel is connected to improve the power factor when it is PF is low. whether we can connect the capacitor panel on D.G. side(? If it is yes means why?

1 Answers   Aricent, Essar,


How many capacitors using in LT panel as per Govt rules?

0 Answers   Electrical Tech,


which type of motor is used in lift ?

7 Answers  






what is the meaning of harmonic in AC waves and when which are prduce and what is the effects on line and give any other information about harmonics

1 Answers  


LT, CC and LMU installed at both the outgoing circuits of 132 kv double ckt transmissio what its means ? and what are there use ?

1 Answers  


Power factor =1.000 at factory in supply. However, PF = 0.8 at motor end. Current = 100 Amp, Voltage = 400 V. What is the power distribution loss? Can I reduce it by adding capacitor at the load feeder?

0 Answers   Accenture,


how vfd drives energy save

5 Answers   PowerTech,


Briefly describe means used by electricity suppliers to influence the flow of active and reactive power in power networks (one for each type)?

0 Answers  


WHAT TYPES OF OIL(STRUCTURE) ARE USED IN POWER TRANSFORMER INSULATION?

4 Answers  


Is it possible to operate a synchronous 2-poles turbogenerator with a still-in-place faulted bar but electrically disconnected ???? If yes, should I act on the other phases as well ???

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)