how many amps in 1 KVA? V=440v, PF=0.8 and FREQ=50Hz
Answers were Sorted based on User's Feedback
Answer / raeworx
SINGLE PHASE CIRCUIT three phase circuit
V(PHASE)= V(LINE)/1.732 KVA = I*V*PF*1.732
= 254V I = KVA/V*PF*1.732
THEREFORE I = KVA/V = 1000/(440*.8*1.732)
= 1000/254 = 1000/ 609.7
= 3.94A = 1.64A
| Is This Answer Correct ? | 10 Yes | 9 No |
Answer / sushant
KVA = (1.73*VICOS PHI)/1000
1 = (1.73*440*I*0.8) / 1000
I=1000/(1.73*440*0.8)
= 1000/608.96
I = 1.64 A
There is no ralation between volt,ampere & freq
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / deepak
KVA(Apperent Power)=1.732 * Line voltage * line Current(It
is in Three Phase System)
According to above formula
I= KVA/1.732*Line Voltage
I=1000/1.732*440
I=1.312Amp.
Is This Answer Correct ? 7 Yes 4 No
0
Ameerlal
Re: how many amps in 1 KVA? V=440v, PF=0.8 and FREQ=50Hz
Answer
# 13
kva=1.732*v*i*cos
i=kva/1.732x440x0.8
i=1.6A
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / deepak g shinde.
When Kva known I = Kva*1000/V*1.732
I=kva*1000/1.732*440
I=1*1000/1.732*440
I=1.31 Amps
I consider this only for three phase & not for single
phase ,because there is very rare chance of 440v in single
phase.
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / pearl ganesh
kva=1.732*v*I*p.f
I=kva*1000/1.732*440*0.8
I=1*1000/1.732*440*0.8
I=1.640 Amps
| Is This Answer Correct ? | 16 Yes | 19 No |
Answer / suresh m s
kva=1.732*v*i*cos
i=kva/1.732x440x0.8
i=1.6A
| Is This Answer Correct ? | 3 Yes | 6 No |
Answer / pradeep baliyan
I KW = V * A * 1.732 * .8 / 1000
(For 3 Phase)
Kva = V*A*1.732/1000 (3 phase, V= 415)
Kva =V*A/1000 (1 Phase, V= 220)
| Is This Answer Correct ? | 4 Yes | 12 No |
how power trnafor from 1 point to another point in bus bar ya transmission line( voltage trnasfer from 1 point to another poin)
why generator and t/f ratings given in kva & motor rating is in KW?
what will happen if field winding of Synchronous generators given ac supply
how much Hp motor is required for water suction pump in home uses ?
draw vector diagram and +ve,zero sequence diagram of symmetrical three phase fault.
Is there any relevant technique to produce power from light and heat energy of the sun simultaneosly from same rays of light?
before transformer oil dielectric strenght tests are taken the oil should be allowed to settle to remove option 1 air bubbles 2 gasses 3 contamination 4 water
Which level of the Transformer oil got dielectric strengh? And why?
What will be the full load current of 60KVA UPS. Suggest for this formula.
In the ACB breaker capacity is 2000Amp but this each phase taken 1250 But total beldibg load is 600amp or 700amp watt is the problem
what will happen if OLR CT in all phases are short circuted
Why auxiliary transformers are not connected in parallel in primary stations?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)