How to convert KVA rating into HP rating?
Answers were Sorted based on User's Feedback
Answer / sheeraz ali
It depends upon the power factor,
As 1HP =746 W =0.746 KW
and
apparent power (KVA)= Active power (W) / P.F
if P.F is 0.8 then,
KVA=0.746 / 0.8 = 0.9325
if P.F is 0.9 then,
KVA=0.746 / 0.9 = 0.8288
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / sheeraz ali
sorry its
apparent power (KVA)= Active power (KW) / P.F
| Is This Answer Correct ? | 2 Yes | 0 No |
KVA is apparent power and HP is real power.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / simon
For e.g 1 Kw=1000Wt
1000Wt=250 v*4 Amp (in 1 Phase)
1000Wt=440v*2.27Amp(in 3 Phase)
1 Hp=735.5Wt
| Is This Answer Correct ? | 0 Yes | 1 No |
What are the Formula of computing Back up Time of 500kVA UPS with 4 Battery Banks, each bank composed of 43 pcs of Batteries 12V150Ah. How to compute the Back up Time of UPS? We have also 3X500kVA UPS running in Parallel same composition as I write above.
How to calculate Grid rotor resistance(GRR) losses in slip ring induction motor?
How to calculate battery back up time for a 400 AH battery bank installed in telecom shelter for a load of 20 Amps and time taken to fully charge this battery bank?
some meggers have three terminals. wat is the real function of the earth terminal?
1.what is difference between ATS & STS main use. 2.what is difference between ACB& VCB With symobles,and main partes, manimum range. 3.How many types of relays and main function.
what is the difference between a hooter and a mcp
Brushed alternator is also called dc generator ? its true or false ?explain it ?
the question is about buchloz relay why we called it buchloz relay
When we use air circuit breaker, it has O/L protection ,time delay SC protection, Instataneous SC protection & ground fault protection. They all have some setting range. But what is the suitable/allowable setting for the above protection which will be safe for the equipment? For example-O/L protection setting have a range of (0.4,0.45,0.5,0.55,0.6,0.65,0.7,0.8,0.9,1.0)xIn Time delay SC protection have a range of (1.25,1.5,2,3,4,6,8,10,12)xIn Time delay setting is 0.02,0.1,0.2,0.3,0.4 Instataneous setting is fixed to 20xIn Gound fault setting is given 100A,300A,600A,900A,1200A This setting are for 2500A ACB. So what will be the basic allowable setting for the above protection? is there any formulae to calculate this<
How Arc Produced in Circuit Breaker When the contacts of the circuit breaker open.
Please tell me the formulaes while designing a substation for power Calculations in designing a 33 KV Substation?????
why do the core of transformer saturates???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)