According to general circuit diagram of 1-Phase t/f , why
the primary is not get short circuited ,even though the
supply terminals both are directly connected through
primary winding?
Answers were Sorted based on User's Feedback
Answer / pratheesh
How it will get shortcircuited. The primary winding has
impedence(Resistance+inductance).
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / t0cableguy
Magnetic induction is the way a transformer works, in all
reality it works somewhat like a motor to produce the
voltages. Ex. (step down transformer) The windings twist
around each other producing a 1:60 voltage drop.. meaning
for every 1 high voltage winding there are 60 low voltage
windings. the high and low voltage windings are isolated
from each other therefore a magnetic field is produced (the
product). That is your load for whichever voltage is feeding
the transformer , and the "source" side of the transformer
works SOMEWHAT like a magnetic induction motor at that point
and becomes your "source" of low voltage.
| Is This Answer Correct ? | 0 Yes | 0 No |
To understand this correctly take the example of a simple
bell in your home. It has only 1 winding and due to this
the solenoid acts and rings the bell. But the number of
turns should be correct or if less then shortciruit may
occur and if more then it will not work the bell.
In general the formula V secondary/ V primary = Turns
secondary / turns primary. i.e. Vs.Tp = Vp.Ts
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / veeru
there is a chance of short circuit even vith
resistance,inductance.
The reason is that just the current flows through tye
path "v+,primary wdng,v-".
just path should be closed to flow current.It is the
basic rule in electricity..
| Is This Answer Correct ? | 0 Yes | 1 No |
motor is 12.5hp after starting few minets motot get hot? why?
where solid grounding and where grounding through ngr done and why?
How to find Cable size? Caterpillar generator produce (Two generators) 127*2=254 amp at 11 kv . What would be the cable size (XLPE) to supply 256 amp at 11 kv? Air or surrounding Temperature is 32 degree C. Cable will go under ground at 2.5 feet depth. Group Rating Factors is 3 cables. Clearance between cables is 7 cm. Soil Temperature (Ambient) 28o C Soil Thermal Resistivity is 1.2 K.m/W I would like to use 3 separate single core instead of using 3 core cable. Some says I should use three separate single core 120RM cables. Some says 70RM .some says 95. I m totally confused. Is there ant specific rule to determine cable size? What would be the LT cable size to flow 500 Amp current? Ifte My e mail address is ifte13@yahoo.com Anyone please send me the answer to my e mail address, i will be very glad.
Is a current transformer step up or step down ?
How to take Vector group test of Transformer?
16 Answers Sunflag Steel, Zuari Cements,
how to test reverse power trip?
which type of questions asking for solar companies?
Why the outpet og DG is 415V not 440V?
Application Comparison between 22KV (UE)and 33KV (E) system. Are we allowed to use 33KV (E) cable in lieu of 22KV (UE) cable. What are the technical disadvantages.
FACP Means
What are the fire Estingushers use in electrical fire?
suppose MCC (Motor control center)panel work on field the relay on this damage or not work and earth fault occurs in this and no indication in relay panel given below. than MCB trip or not and what effect the panel how find relay will damage or not work.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)