Answer / pramod sahoo
To protect the CT from static voltage surges resulting in
insulation falure.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sheik hussain
if secondary side open ct act as step up transformer so flux
is increased ,for that insulation is not withstand so
vibration and high voltage occurs thats why we should kept
the sec terminals closed condition..
actually ct is not have a pry turn it have only sec tunas,
pry side is like busbar cable conductor ect.,so when s1,s2
is open it mutual inductance is occurs so act as a step up
transformer.. the flux is incresed,insuation get failure
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / simon
The Eddy current's value is too high so the sec side of X-mer is grounded.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / abb
Open Circuit secondary side of the Current Transformers
causes saturation due to high voltage induced.
Is This Answer Correct ? | 0 Yes | 0 No |
Shorting is done ,when the ct is not in use or in case of
spare ct, to prevent development of high voltage in
secondary.Grounding is done to remove the influence of high
primary voltage due to capacitance between primary and
secondary, and insulation failure.
Is This Answer Correct ? | 0 Yes | 1 No |
Power Factor Controller
how will reduce the voltage. if 12volt/250ma transformer toreduce 6 volt
What is open delta Xformer? It's adavntages & Use?
CAN 50Hz transformer work at 60 Hz power supply? if yes how it is possible?
what is the significant for using two types of voltage(line voltage & phase voltage)
how i meggar value of 11kv alternator winding.and with meggar.
Two alternators say 1 & 2 are poised to parallel operation. But at the time of paralleing alternator 2 gets out of the system by tripping Earth fault relay. Please send me reply why this is happening?
difrent between vcb acb sf6 and mccb breakers
why the earth terminal of the three pin plug we are using bigger than the others?
What are the classifications of heating element?
What will hapen if we run generator below 47.6hz frequency?
why battery set is required for D.G.set?