I need the proper answer on :-
What is the Earthing Value as per the standard for Raw
power and UPS Pit and in panel /DB N-E value ???
Answers were Sorted based on User's Feedback
Answer / k.p.sharma
The Earthing Value as per the standard for Raw
power and UPS Pit SHOULD BE LESS THAN 2 OHM and in
panel /DB N-E value SHOULD NOT BE MORE THAN 5 VOLT.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / rathod manhar
For raw power and UPS pit the earth resistance value is
around 1 ohms and N-E value is 1-0.5 ohmsfor good earthing.
Is This Answer Correct ? | 2 Yes | 0 No |
what is the principal of braker
What is notching in dc machine?
State the other types of Air Conditioners?
i want to know d working mechanism of tafe tractors next i like to know d engine type of apache bighs can anyone help me
How much of the total hydro power potential has been exploited so far in india?
In CTs tan delta point should be earthed , what is the reason behind it?
We have 250 KW x 2 motors, which are load from 25% to 100% varying load in every minute , so how can we compansate the power factor. pl give your opinions on the above subject.
While performing load test on DC SERIES MOTOR, does the voltage decrease slightly. Why?
what are the effects when a salient pole alternator is run at high speed like 3000 r.p.m?
what is the method of electric earth for the protection of low voltage electric equipment
1 Answers MacLellan, Shiva Corporation, Siemens,
why we use the fuse in only one wire? althrough in ac current the current flows in both directions. why the neutral wire can be taken half the magnitude of phase wire while same current returns from neutral wire?
What is maximum power transfer theorem?