Answer / khursheed
Metering CTs have saturation restrictions to protect the
measuring instruments, but Protection CTs has higher limits
of saturation.
Is This Answer Correct ? | 25 Yes | 1 No |
Answer / k.prabhakar reddy
Metering CT:Wil be used for the purpose of measuring of
current only.
Protection CT: Wil be used for the purpose of protection of
the power devices
Is This Answer Correct ? | 15 Yes | 7 No |
Metering cts used only in measuring secondary currents(in
view of primary current),no knee point voltage ,winding
resistance is low.
Protection cts r used incase of any faults in d system,knee
point voltage is there,winding resis. is high.
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / ullas
metering ct= this belongs to accuracy class .1, 1 etc.
and used to measure current, can be indicated in ammeter
and also can be given to an energy meter to measure kwh.
the cts belong to this class is not used for back up
protection or main protection .
protection cts== this cts can be divided in to backup
protection cts and main protection cts.
backup protection cta belongs to calss 5p10, 10p10, 15p10
etc. these ct are used to give over current and earth fault
protection.
special protection cts= this is used for differetial, ref
protections.class ps
oe main thing you should understand is that these are
coming as different cores of a single ct.
that means a ct with 3 or 4 cores.
each core is meant for different purposes like metering,
backup, special (main) protecton.
i think u ca understand better now.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / vijayakumar
Metering CT:Wil be used for the purpose of measuring of
current only.
Protection CT: Wil be used for the purpose of protection of
the power devices
Is This Answer Correct ? | 5 Yes | 4 No |
Answer / lalit barsker
IN METERING C.T. SECONDARY(LOW VOLTAGE SIDE) OF THE CT IS
CONNECTED TO THE METER I.E. AMMETER WATTMETER e.t.c.and in
protection C.T. SECONDARY(LOW VOLTAGE SIDE) OF THAT CT IS
CONNECTED TO RELAY FOR PROTECTION PURPOSE WHEN FAULT OCCURS
RELAY SENSE IT AND C.BREAKER TRIPS.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / krishnan
The class between metering and protection will be diffrent.
Is This Answer Correct ? | 4 Yes | 5 No |
Answer / cnsubudhi
metering ct exclussively used to measure electrical
parameters.Where as protection ct used to protect the
devices.
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / karthikeyan
Metering CT: Wil be used for the purpose of measuring of V,
A, PF, Frequency etc.
Protection CT: Wil be used for the purpose of protection of
the power devices
Is This Answer Correct ? | 9 Yes | 12 No |
Answer / venkatesh
ct measuring the currentand protection ct for
busbar,overcurrent.
Is This Answer Correct ? | 0 Yes | 3 No |
In a transformer, the hysteresis and eddy current losses depend upon 1.load current 2.maximum flux density in core 3.type of lamination 4.supply frequency The correct statements are (a) 1 and 3 (b) 2 and 3 (c) 1 and 4 (d) 2 and 4
For a CT the number of turns in the primary winding is.........
If OLTC is in manual position there is chance to variation of voltage(Low or High)?
what is the difference between high impedance and low impedance circuit?
what is the working of vfd drives.
Why positive terminal of DC 48V was earthed?
1. If 8.35%Z means the percentage impedance of 132kV-line from power company, we will like to reconfirm its base capacity.
What is partial discharge in power cable?
1.why motor rating in kw instead of KVA? 2.why alternators rating in KVA instead of KW?. 3.why transformer rating in KVA instead of KW?.
how starting current in motor is reduced in case of motor in star connection.
y we are used signal conditioner in capacitive transducer
What the full form of KVARs