what is differnt between metering CTs an protection CTs
Answers were Sorted based on User's Feedback
Answer / khursheed
Metering CTs have saturation restrictions to protect the
measuring instruments, but Protection CTs has higher limits
of saturation.
Is This Answer Correct ? | 25 Yes | 1 No |
Answer / k.prabhakar reddy
Metering CT:Wil be used for the purpose of measuring of
current only.
Protection CT: Wil be used for the purpose of protection of
the power devices
Is This Answer Correct ? | 15 Yes | 7 No |
Metering cts used only in measuring secondary currents(in
view of primary current),no knee point voltage ,winding
resistance is low.
Protection cts r used incase of any faults in d system,knee
point voltage is there,winding resis. is high.
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / ullas
metering ct= this belongs to accuracy class .1, 1 etc.
and used to measure current, can be indicated in ammeter
and also can be given to an energy meter to measure kwh.
the cts belong to this class is not used for back up
protection or main protection .
protection cts== this cts can be divided in to backup
protection cts and main protection cts.
backup protection cta belongs to calss 5p10, 10p10, 15p10
etc. these ct are used to give over current and earth fault
protection.
special protection cts= this is used for differetial, ref
protections.class ps
oe main thing you should understand is that these are
coming as different cores of a single ct.
that means a ct with 3 or 4 cores.
each core is meant for different purposes like metering,
backup, special (main) protecton.
i think u ca understand better now.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / vijayakumar
Metering CT:Wil be used for the purpose of measuring of
current only.
Protection CT: Wil be used for the purpose of protection of
the power devices
Is This Answer Correct ? | 5 Yes | 4 No |
Answer / lalit barsker
IN METERING C.T. SECONDARY(LOW VOLTAGE SIDE) OF THE CT IS
CONNECTED TO THE METER I.E. AMMETER WATTMETER e.t.c.and in
protection C.T. SECONDARY(LOW VOLTAGE SIDE) OF THAT CT IS
CONNECTED TO RELAY FOR PROTECTION PURPOSE WHEN FAULT OCCURS
RELAY SENSE IT AND C.BREAKER TRIPS.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / krishnan
The class between metering and protection will be diffrent.
Is This Answer Correct ? | 4 Yes | 5 No |
Answer / cnsubudhi
metering ct exclussively used to measure electrical
parameters.Where as protection ct used to protect the
devices.
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / karthikeyan
Metering CT: Wil be used for the purpose of measuring of V,
A, PF, Frequency etc.
Protection CT: Wil be used for the purpose of protection of
the power devices
Is This Answer Correct ? | 9 Yes | 12 No |
Answer / venkatesh
ct measuring the currentand protection ct for
busbar,overcurrent.
Is This Answer Correct ? | 0 Yes | 3 No |
What is the purpose of shunt trip in ACB function?
During FEED, you will have all the information with regards to cable. How will you calculate the MTO for MV and LV Cables? what are your considerations?
In what situations relays are used in Circuit breaker? In Above what rating of Circuit breaker the relays are used? Why relays are not used for CB like MCB?
How to specific gravity of battery will check, i didnt saw any hydrometer. & say me how to dip into the battery what are the specifications are given in the hydrometer?
What is neutral earth voltage of transformer and what should be the value
why induction motor having low power factor at starting time and high at full load.
The speed of a dc motor can be controlled by the variation of 1. armature voltage. 2. field current. 3. armature circuit resistance. 4. angle of brush shift. Which of the statements given above are correct? (a) 1,2 and 3 (b) 2,3 and 4 (c) 1,3 and 4 (d) 1,2 and 4
kVA rating of ordinary transformer is increased when connected as an auto transformer because A transformation ratio increased B secondary voltage increased C energy is transferred both inductively and conductively D secondary current increased
operation principle of a generator? Gss, Diesel and HFO which is better and why?
why we cant use AC supply products in DC supply?
What are the different circuits in thermal power plant?
what is the difference between 11kv and 13.8 kv? why we can't used one of these 2 sources?