1.generator rated as 1000 mva,11kv .8 pf what will 0.8 pf
will indicate?
1.max pf it can supply 2.min pf it can supply
like this 4 options there what is answer.explain
Answers were Sorted based on User's Feedback
the above mentioned genrator Ans is 1.
it can supply max. load i.e 0.8 pf means 80 percent of rated
1000*0.8=8MW.
Is This Answer Correct ? | 11 Yes | 2 No |
i agree with Mr Reddy.
Generator rated at 1000MVA at 0.8 pf 11Kv
In terms of KW the prime mover had been designed for this Gen is 1000 MVA X 0.8 = 800kw, any thing more can destroy your prime mover in the long run
now the alternator part is 1000 MVA AT 11KV
The max amps it can carry is 1000000/1.732/11000= 52.5A /phase
now you can operate the generator at any pf you want as long as you do not exceed 52.5 amps per phase.
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / sreenivasalareddy
I will deliver (generator design)800mw power wether it
running at .8 PF or unity pf
When Generator runnig at upf we should alert we should not
load alternator to its rated current
Because your out put power will become 120 % almost ,Which
is not design for this load (Primover)
As for as my concerned pf is restrited to protect promover
and alternater eigher way
Is This Answer Correct ? | 5 Yes | 2 No |
What is Primary and Secondary Injection Test of CT and Relay.
How to calculate the electrical load for a standard telecom BTS shelter and capacity of DG set required to cater to this load?
3 Answers Bhel, INDUS, Indus Towers,
What are the safety equipments you should use while you are in a hvac switch yard
1 Answers GPSC Gujarat Public Service Commission,
How line capacitance & line inductance varies with increase in height tower.
what happens if dc supply is given to the transformer?
Why battery rooms painted with dark colour
1 Answers BAL, MSETCL Maharashtra State Electricity Transmission Co Ltd, Polycab,
what is submersible pump?what is different between motor and sub motor?
How a generator is positioned in a hydroelectric power plant?
What is genrally the % Impedance of a Dg set? How can we calculate Earthing conductor size for a DG set?
what is REF relay?
why in a swquence network representation, the negetive sequence generated voltage is taken as zero?
Relay setting for earth fault of reciprocating and centrifugal compressor motor feeder.Setting will be different or same?