1.generator rated as 1000 mva,11kv .8 pf what will 0.8 pf
will indicate?
1.max pf it can supply 2.min pf it can supply
like this 4 options there what is answer.explain
Answers were Sorted based on User's Feedback
the above mentioned genrator Ans is 1.
it can supply max. load i.e 0.8 pf means 80 percent of rated
1000*0.8=8MW.
| Is This Answer Correct ? | 11 Yes | 2 No |
i agree with Mr Reddy.
Generator rated at 1000MVA at 0.8 pf 11Kv
In terms of KW the prime mover had been designed for this Gen is 1000 MVA X 0.8 = 800kw, any thing more can destroy your prime mover in the long run
now the alternator part is 1000 MVA AT 11KV
The max amps it can carry is 1000000/1.732/11000= 52.5A /phase
now you can operate the generator at any pf you want as long as you do not exceed 52.5 amps per phase.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / sreenivasalareddy
I will deliver (generator design)800mw power wether it
running at .8 PF or unity pf
When Generator runnig at upf we should alert we should not
load alternator to its rated current
Because your out put power will become 120 % almost ,Which
is not design for this load (Primover)
As for as my concerned pf is restrited to protect promover
and alternater eigher way
| Is This Answer Correct ? | 5 Yes | 2 No |
how to give earthing in ships?
when voltage increases then current also increases then what is the need of over voltage relay and over current relay? can we measure over voltage and over current by measuring current only?
ell me capacitor bank chossen formula.load in KW
how to decide the capacity of accl
what will happen if we use earthing inplace of neutral for domestic energy meter
5 Answers Polyplex Corporation Limited,
we all know voltage is a force(emf), and the force always devides if 2 or more than2 loads are there but why does the voltage remains same is parallel, it must devide na ???
how does high earth to neutral voltage affect electronic equipment?
WHY HOLDING CONTACTOR OF MOTOR STARTER IS CALLED NO VOLT COIL.
why grid failure happens?
How to find the maximum load, that can be supplied by a transformer.....
how much current capacity 250 amp. mccb please tell me about whats are the reasons to trip 2 or 3 times in a night. and what are the steps to short out this problem
what is the necessary of using inductance property in transmission lines even through resistance is used to opposes the high current flows in that?????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)