what is the procedure to carry out BDV test of a
transformer ?
Answers were Sorted based on User's Feedback
Answer / p.s.suresh
1. first we will take filltered oil in test kit.
2. then maintained 2.5mm gap between electrode and applying
rated 40 & 60 Kv for 1 minite .
3. the above test withstood for 1 minite its ok for
energiseing the transformer.
Is This Answer Correct ? | 22 Yes | 9 No |
Answer / c.b.sharma
1.first we will take filltered oil in test kit.
2. then maintained 2.5mm gap between electrode and applying
rated 40 & 60 Kv for 1 minite .
3. the above test withstood for 1 minite its ok for
energiseing the transformer.
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / vinod
1)Take transformer oil sample from both bottom and top
section with suitable container on dry day
2)Adjust the BDV kit electrode for 2.5 mm and ceck with
gauge, increase the voltage till breakdown occur
3)Now a day automatic tester is available it will take
consicutive five readings with stiror. third reading will
be the BDV.
Is This Answer Correct ? | 8 Yes | 3 No |
what is the function of choke in tube
Why the transformer rating is denoted in VA rating why not in KW
how to calculate Amp, 2 different Amp of batteries? Example: No. of Batteries = 2 Battery voltage = 12V 1st Battery rating = 17AH 2nd battery rating = 30AH between parallel connection then output volt 12v Amp?
How does HT work & Voltage required?
why the voltage level in transmission line are in multiple of 11kV, 22kV, 33 kV etc..( i.e., 220 V )?
If we say that an cable of size 3.5X 50 mm sq. can take current upto 140 amps,is it the current of single core of the cable or of all the cores jointly.
What is the formula to find out the kvar required to improve the powerfactor from .85 to .99 at 1500kw, 415v.
What is BKW of Motor. And what its significance
What is the difference between shortcircuit current, rated current of cable & MCB with example? What will be the size of cable required for 5.5 KW motor (Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.
There are a trformer and an induction machine. Those two have the same supply. For which device the load current will be maximum? And why?
Why don't connect earth wire to elcb?if earth fault occur,how will detect it
1 Answers TATA, Tata Communications, Telecommunications,
Is it possible to make a 5P10/ CT Ratio 50/1A Burden 5VA