Befor synchronissation of Generator what test to be carried
out.pl.specify with reason.
Answers were Sorted based on User's Feedback
Answer / vijay
Before Synchronisation mainly three conditions
(voltage,speed/frequency & Phase sequence) has to be
checked which are within the limits. Reason to monitor when
any one on this parameters found not in unique, DG set's
not getting synchronised.
If the synchronisation happened in unconditional status, it
causes unbalance current will flow in the operation and
load sharring is not even. To eliminate this kinds of
occurence Dark lamp test was carried out before execution.
Is This Answer Correct ? | 9 Yes | 1 No |
Answer one is mostly correct. Two other factors are important. 1) the winding type (e.g. 2/3 or 5/8) as this can affect circulating neutral current. 2) phase angle at time of synchronising must be within limits to prevent high currents to pull DGs into synch.
For answer two - load sharing equipment can allow DGs of different ratings to be used in parallel. Frequency is important not RPM. The number of poles in an alternator can vary requiring a different RPM for the same frequency.
Another important factor iis governor response to load changes
Is This Answer Correct ? | 0 Yes | 0 No |
BOATH THE DG'S ARE EQUAL RATING(KVA)
BEFORE SYNCHRONISING THE TWO DG'S TO CHECK 1)BUS VOLTAGE
2) FREQUENCY 3) RPM
Is This Answer Correct ? | 0 Yes | 4 No |
What is superposition theorem?
write a c++ code that receives an integer number and display the sum of the number and its revers integer?
what is the function of a circuit breaker ?how does the circuit breaker function during normal operation of an electrical system
what the Microsoft .NET framework is?
How many type of ht insulator with name
1 Answers Bhushan Power Steel,
We have .ht motor which is 60Hz.we run on 50Hz.so that it's speed reduce but we had one prob.that motor winding temp increase up to 135 deg.we want reduce this temp.what to do?we arrange ext.cooling fan but not much effect.we want reduce this temp. Inhouse without affecting much.cost. also don't want reWINDING OF MOTOR?
A generating system will have a total capacity of 300 MW. Find the probable forced outage when the capacity is supplied by two 150 MW units. The operating probability of all units is P=0.98 and forced outage probability rate Q =0.02 .
Our Company's Contract Demand is 110 kVA. We use 12 Capacitors each of 12.5 kVAr Capacity to maintain Power Factor of 0.99. So, what steps should we take so that our Contract demand does not exceed 110 kVA?
which is more dangerous AC\DC supply
Why effective AC resistance is more than DC resistance of a transmission line?
How the earth fault relay works please explain?????????
What is PEC??Applications........