Dear sir,
we are getting voltage fluctuations suddenly for 2 or 3
minutes again it becomes normal. we checked each and every
connection some times we are getting 110 volts like that
from earth to neutral again it is reducing we are getting
supply from 45 kva DG set give earthing properly.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Unbalanced load can not be responsible for 110 V between
neutral and earth.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
Voltage between neutral and the earth indicates a loose
connection/joint in the neutral wire as neutral extends only
upto the point of loose connection.
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / manoj dubey
generally voltage between neutral and earth occurs when
there is unbalance distribution of load in all three
phases. first check load balancing on phases. also check is
there any single phase heavy load is switched ON at the
time when voltage increases between neutral and earth.
Is This Answer Correct ? | 1 Yes | 1 No |
what is meant by leakage current of a capacitor?
In an electrical power supply,why if neutral phase of a 3phase supply fail over current occur but if it's single phase supply neutral phase fail low current occur?
How much load can be taken for chiller from 1500 kva transformer
what is the formula for building wiring to get the main breaker.
what is form factor?
1.what is bus cuplour and main funtions. 2.what is main function of alternator. 3.how many types of dg oils.
which IS or IEC is used for earthing,breakdown voltage of transformer oil, hv/pd testing and all type of electrical testing
Sir, I need a power supply at 380V. The supply I get in three phase is rated 415V. The total supply I have from the supply company is 70KW. Kindly inform if it is better to use a voltage stabiliser for this purpose or a transformer
Why the underground cables will Punchar? or what is the reason to burst the underground cables?
a)In a 3-phase 4-wire circuit, a circuit breaker is selected to protect the circuit whose highest fault level is 6.6 MVA. Determine the required minimum breaking capacity in kA. (Note: Covert 3-phase power in terms of kA to find answer.) b)Using the below, determine the required minimum making capacity in kA as a “peak value”. Rate breaking capacity (Icn) ka: Icn<= 1.5 Factor = 1.41 1.5
why power generate in 33 kv it will be step down by 11 kv .
Mention the value of earth resistance and factors on which it depends on.