What is loop or pigtail in an impulse line?
Answers were Sorted based on User's Feedback
Answer / k. thirunathan ntpc ramagund
1.PIGTAIL IS USED ONLY IN STEAM LINE WHICH HELPS TO CONVERT
STEAM VAPOUR PHASE IN TO LIQUID WATER PHASE
2. AVIOD HIGH TEMPERATURE DIRECTLY CONTACT
IN INSTRUMENT LIKE PRESSURE GAUGES,PRESSURE
TRANSMITTERS..etc.
3.FINALLY IT REDUCES HIGH PRESSURE INTO LOW PRESSURE AND
AVIOD VIBRATION IN IMPULSE LINES.
| Is This Answer Correct ? | 35 Yes | 12 No |
Answer / solomon
pigtail is also called syphon.It is used to reduce
temperature of fluid like steam before enter in to the
Pressure gauge or Presssure Transmitter for measurement
| Is This Answer Correct ? | 26 Yes | 3 No |
Answer / haridass_drm
My friend, Mr. K. Thirunathan Ntpc Ramagund, all your
points are correct, except
3.FINALLY IT REDUCES HIGH PRESSURE INTO LOW PRESSURE AND
AVIOD VIBRATION IN IMPULSE LINES.
In this point, avoiding vibration is ok, but how the high
pressure will get reduce to low pressure? If like, how can
we use that pigtail for high range pressure
gauge/transmitter?
According to me, this pigtail will be used to avoid the
sudden pressure impact on the gauge/transmitter, created in
the process where it fixed. Because the boiler/vessel/steam
line will be high pressurized, so there is the chances for
sudden variation, the pigtail will safe the instruments if
it used.
| Is This Answer Correct ? | 18 Yes | 4 No |
Answer / habeeb
pigtail reduces velocity of steam,but pressure
same.temperature not effecting the instrument
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / sreekanth
Friends....Pigtail is used only for protection of
instrument from temperature.
For pressure Damping we will use Pulsation Dampners.
Due to the loop, condensate is formed in the pigtail and
some part of fluid cannot be drained and remain in the
pigtail which will prevent the instrument all the time from
temperature from direct contact of the fluid.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / www.islamqa.com/en/
It used mainly in steam services to avoid direct contact
between sensor and high temperature steam.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / suresh m (fcri)
Loop/Pigtail helps provide for tube expansion due to
temperature changes. If tube is straight and directly
inserts into the pressure transmitter (which is also
rigidly fixed to a support), there will be streses in tube
due to expansion/contractions.
In steam applications, impulse tubes are to drain
condensate back into process line and transmitter is fixed
generally above process line. The same with gas
applications. For liquid applications, the impulse tube
slopes to eliminate gas formation inside which escapes back
to process line.
In both cases, the pigtail/loop will therefore have to be
appropriately directed (either upward or downward
respectively, even as slope is maintained for impulse
lines).
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / m.murali -inst. technoligist
TO AVOID THE SHOCK PRESSURE, IT WORKS AS SHOCK ABSORBER
| Is This Answer Correct ? | 4 Yes | 6 No |
How to zero trim the level transmitter by using foundation fieldbus communicator.
HOW TO CALCULATE WAKE FREQUENCY FOR THERMOWELL???WITH OUT SOFTWARE..
if I did short to both AO connections, channel will burn or what? m sure in AI it will damage to channel. But what will happens in AO?
In which principle Woodward Governor 505 work in power plant? What are the input of Woodward governor 505
what is difference between pressure,flow and level control valve.
Explain bernoulli’s theorem.
Why we use 250 ohm resister in series hart communicator?
how to draw a flowchart for swapping two numbers using bit wise operators?
There are two chlorination tonners both are connected to two pressure swithes and the pressure switch is connected to SOV which operates the valve to changeover the tonner selection i.e if pressure one tonner goes low the other tonner should come in line if it is inautomatic selection design a circuit using relays ?
In my company plc based winders are operated. one day there was a data transmission failure alarm shown on pc. as per sir instruction we have reset master plc but winders were not triped and alarm gone. so what master plc do?
What is DDC-MIS?
How to convert mmWc(mili meter water colam) to tph(ton per hour)?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)