Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Yokogawa mass flow meter shows negative reading...what r the main causes for this problem?...

Answers were Sorted based on User's Feedback



Yokogawa mass flow meter shows negative reading...what r the main causes for this problem?.....

Answer / carl_ellis

Yokogawa mass flow meter shows negative reading...what r the main causes for this problem?...

Impossible to say, because the technology is not stated, nor are the conditions stated.

Yokogawa is a brand name, not a technology, and the reason for a negative flow indication depends on the technology.

Technologies for mass flow (however inferred) are
- multivariable flow meters based on pressure and temperature compensated differential pressure
- Coriolis flow meters
- Vortex flow meters with temperature and pressure compensation
- Thermal dispersion flow meters
which might or might not be Yokogawa products.

The reasons for a false negative flow indication could be quite different for any of the technologies

Conditions like the expected flow rate vs the observed flow rate, medium, medium temperature and pressure, service history, installation details (vertical or horizontal), flow path, type of pump, process function or contiguous piping and its orientation, and configuration elements like low flow cutoff could contribute to an indicated negative flow rate, or operational method of zeroing.

Because it could be that you actually have reverse flow from a thermal syphon or a pressure syphon.

Carl Ellis
Measure First

Is This Answer Correct ?    4 Yes 0 No

Yokogawa mass flow meter shows negative reading...what r the main causes for this problem?.....

Answer / manikanta

Flow will may be in revers direction

Is This Answer Correct ?    4 Yes 1 No

Yokogawa mass flow meter shows negative reading...what r the main causes for this problem?.....

Answer / sarin

HP LP Ports will be interchanged. High pressure is coming in LP Side.

Is This Answer Correct ?    2 Yes 2 No

Post New Answer

More Instrumentation Interview Questions

A differential transmitter is calibrated to measure the flow of lquied, explain what wil happen if the fluid is not pure but contains some bubble?

2 Answers  


typical loop drawing of a simple feedback control comprising of one transmitter and one control

0 Answers  


1. what is 3 point calibration & 5 point calibration? 2. If we use hart communicator to set the LRV & URV of a smart transmitter, did we calibrate the transmitter? why? 3. Make a complet list if meterials needed to properly connect a pressure gauge to a steam pipe using 1/2 inch stainless steel tubing. The gauge connections is 1/2 inch NPT-M and the steam pipe tap has a 1/2 inch female coupling, compression fittings are use. 4. What are the tools in loop checking? 5. What would the ISA symbol of a square root extractor look like? 6. What would you do to completely prepare for the configuration? 7. What safety measures must you undertake when doing configuration? 8. what are the two most commonly use programming languages used when we configure a PLC? 9. What would you do if you accidentally skipped a step in the configuration procedure? 10. How would you know if the configuration were sucessful? 11. Name at least 3 selections available when we configure the burnout protection of a controller?

3 Answers   EI Electrotechnical Institute,


Name some of the common protocol use in automation.

3 Answers   Empower,


how can i calibrate the temperatuture gauge used by temperature bath(dry block) i mean step by step procedure?

0 Answers   Texas,


What is the standard height for stancion supports? and what is the standard mounting height for different transmitters?

11 Answers   Samsung,


what is see back effect?

9 Answers  


what is load line in control valve?

3 Answers   Boral, Qatar Petroleums,


what are the possible reasons if a control valve fails to open/close?

1 Answers   DEWA,


difference b\w a transducer and a sensor

4 Answers  


Wht is Dry Leg Calibration and Wet Leg Calibration?

2 Answers  


why we use impulse line of flow transmitter at 45 deg. angle both side of orifice plate.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)