Answer / ariel
- Draw the per phase diagram of the system
- Express all impedance in per unit values
- Choose a common MVA base and express all Zpu on the
selected common MVA base
Znew= Zpu(MVA base/ MVA)
-Calculate the total per unit impedance of the system
using circuit principle
- Calculate the fault power
MVA fault= MVA base/ Z total per unit
I fault = MVA fault/ 1.73* V
| Is This Answer Correct ? | 14 Yes | 5 No |
Answer / mak
The fault current of a power transformer will depend on the following;
Transformer Rating (in KVA/MVA)
per unit impedence of the transformer (%p.u.)
line/phase Voltage (VL/VP)
the following formula can be used to find the fault current on the secondary side of a transformer
Fault Current = Transformer Rating /(per unit impedance x phase voltage)
The Values of Transformer Rating, per unit impedance & phase/line voltage will usually be mentioned on the transformer rating plate / data sheet
As an example a 500kVA, 11kV/400V/3-Phase/50Hz transformer with 5% p.u impendence will have the following fault levels on the secondary side
Fault level = 500/(5%)=10000kVA
Fault current = 500/(5% x 400 x 1.732) = 14.4 kA
Remember to use 3phase voltage!
| Is This Answer Correct ? | 3 Yes | 4 No |
Why there is a current in neutral line
Why compensation is necessary in feedback control system?
For 7.5HP motor 2880rpm 415VAC Connected with Pressurisation Fan we used Star Delta Startor why not we use DOL startor
what is relation between vector group of transformer and its load hormonics?
what is the difference between Central Battery System and UPS in applications and uses? and why UPS suitable for Computers and central battery for emergency lighting?
why power dissipation is due to low frequency?
difrent between vcb acb sf6 and mccb breakers
In an ammeter used for measurement of current, what is the meaning of the representation of range as '0-50-300'?
Why we are mostly using a single 3-phase transformer instead of three 1-phase transformers?
a induction motar has 30-35% exciting current at no load but in transformer it is only 2-3% ofbrated current why any reason?
What is Surge arrest? How it work?
what should be the minimum rating for using HT Motors?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)