Write the formula for Fault MVA, Fault current, Base MVA.
Answers were Sorted based on User's Feedback
Answer / ariel
- Draw the per phase diagram of the system
- Express all impedance in per unit values
- Choose a common MVA base and express all Zpu on the
selected common MVA base
Znew= Zpu(MVA base/ MVA)
-Calculate the total per unit impedance of the system
using circuit principle
- Calculate the fault power
MVA fault= MVA base/ Z total per unit
I fault = MVA fault/ 1.73* V
| Is This Answer Correct ? | 14 Yes | 5 No |
Answer / mak
The fault current of a power transformer will depend on the following;
Transformer Rating (in KVA/MVA)
per unit impedence of the transformer (%p.u.)
line/phase Voltage (VL/VP)
the following formula can be used to find the fault current on the secondary side of a transformer
Fault Current = Transformer Rating /(per unit impedance x phase voltage)
The Values of Transformer Rating, per unit impedance & phase/line voltage will usually be mentioned on the transformer rating plate / data sheet
As an example a 500kVA, 11kV/400V/3-Phase/50Hz transformer with 5% p.u impendence will have the following fault levels on the secondary side
Fault level = 500/(5%)=10000kVA
Fault current = 500/(5% x 400 x 1.732) = 14.4 kA
Remember to use 3phase voltage!
| Is This Answer Correct ? | 3 Yes | 4 No |
Can we parallel lise the secondary side of the two similiar transformers with same voltage ration, imp, but with different vector groups.. ( for ex. 11 KV / 6.6KV two trfs but different vector groups can we parallelise both of them ,, what happens if we parallelise them
why shunt capacitor is connected
what happens when the transformer is connected to DC supply?
HOW TO CUT A CAKE IN 8 PIECES IN 1 STROKE
please I wont know how to calculate the vector group for power transformer ZNyn11 best regard.
what is the synchronous timer ? and it applications.
what is ACB
WHY DOES NEUTRAL DO NOT CARRY EVEN THOUGH IT CARRIES RETURN CURRENT?
how can we measure the import power and export power in the same line?
how determine base of given number like 302/20=12.1
HOW TO FIND OUT 1. LINE CURRENT, 2. PHASE CURRENT IN AN ALTERNATOR / TRANSFORMER WHICH IS FEEDING A I)STAR LOAD ii) DELTA LOAD, USING A CLAMP METER. NORMALLY WHEN WE USE CLAMP METER IN A DG SET THEN WHAT DO WE GET?? PHASE CURRENT OR LINE CURRENT.
If I have a LT panel 3ph, 415V, 50Hz which demand load-600kw, how we can calculate its body earth strip size.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)