I have 500A load (WHICH IS SEPARATE MDP PANEL),an MCC panel
with 4000A Breaker.Already I have 2500A load.Can I connect
this load directly to the Busbar since I have PROTECTION IN
MY MDP Panel ?
Answers were Sorted based on User's Feedback
Answer / jagadisha.n bmsit
ya we can..
Actual rating of the motor is 4000A and it was carrying
2500A load since if we connect 500A tio same busbar it
becomes 3000A so it can handled both the load but the prob
is if fault occured in 1 line both the line will trip..
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / santosh bangar
no , because it will trip 2500 A load if fault occur at MDP
it is possible if MDP have it's breaker to clear fault.
then you can connect to MCC bus
| Is This Answer Correct ? | 0 Yes | 0 No |
Dear friend.
Mathamatically it looks possible but bofore making this
arrangment the other factor which you need to consider.
1. The Rating of a transformer.
2. the Ir seeting of a Breaker.
3. Total contract demand if you are using local electricity
board power.
4. change in OT & WT setting.
by checking all the above peramiters you can go ahead.
| Is This Answer Correct ? | 0 Yes | 1 No |
How can we calculate the resistance of earthing & how can we control it?
what is reason in mv breaker the control supply voltage is dc not ac?
How to solve the problem of low voltage at consumer end in distribution system if one phase come low voltage of transformer
What is required of exietation to the alternater.
Why does increasing the magnetic flux in the main field of a d.c motor cause the armature current to reduce??
If a surge divertor is required to be protected by 32 amp C Curve Circuit breaker does this limit the amount of protection from surges that you will acheive
In a parallel circuit dc circuit with two resistors, if you know the voltage, amperage, and one resistors ohms, what formula is used to find the second resistors ohms?
How much allowable difference current between on three phases Dear sir, We have a 1870 KW HT motor, 11 Kv supply,FLA-120A,2870 rpm,2-pole squirrel cage induction Motor.And stator is connected in star connection with Liquid resistance stater to limit the starting current.It has coupled with Centrifugal air compressor.My question is it is loading 73% of FLA taking R-phase 86.7 A, Y-phase-85.4A,B-phase- 78.3A.why the B phase current is that much of difference.Is it allowable, or any one tell me how much allowable current.If any method to calculate.
How to test REF relay testing for LV panel as per Kahramaa standard?
Name the test signals used in control system
what r the checklist while installing 500 kva transformer
how bucchos relay works in a transformer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)