I have 500A load (WHICH IS SEPARATE MDP PANEL),an MCC panel
with 4000A Breaker.Already I have 2500A load.Can I connect
this load directly to the Busbar since I have PROTECTION IN
MY MDP Panel ?
Answers were Sorted based on User's Feedback
Answer / jagadisha.n bmsit
ya we can..
Actual rating of the motor is 4000A and it was carrying
2500A load since if we connect 500A tio same busbar it
becomes 3000A so it can handled both the load but the prob
is if fault occured in 1 line both the line will trip..
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / santosh bangar
no , because it will trip 2500 A load if fault occur at MDP
it is possible if MDP have it's breaker to clear fault.
then you can connect to MCC bus
Is This Answer Correct ? | 0 Yes | 0 No |
Dear friend.
Mathamatically it looks possible but bofore making this
arrangment the other factor which you need to consider.
1. The Rating of a transformer.
2. the Ir seeting of a Breaker.
3. Total contract demand if you are using local electricity
board power.
4. change in OT & WT setting.
by checking all the above peramiters you can go ahead.
Is This Answer Correct ? | 0 Yes | 1 No |
How the cable size for a motor is decided
will three phase energy meter run without one phase
What are the advantages of speed control using thyrister?
what happens when the phase and earth wires comes in contact? and why
why substation ratings are multiple of 11 means 11\33 kv substation
what is PPI DB?
2 Answers Priyanka Electricals,
what is different between IP55,IP54 and IP66?
2 Answers ABB, Global Industries,
In power point wiring,often,we use less size of earth wire compared to phase & neutral wire and we use big size pin in pug top. how is it justified? can we use small size cable for earthing?
Define what is the function of anti-pumping in circuit breaker?
why transformer is rated in kva instead of kw?
what is inrush curent.
During the testing of Electrical Equipment the test cables should not touch the equipments. For that testing engineers use to cotton rope to hang the cable from measuring Equipment to testing equipment terminal. Please explain the technical reason for this practice.