During the testing of Electrical Equipment the test cables
should not touch the equipments. For that testing engineers
use to cotton rope to hang the cable from measuring
Equipment to testing equipment terminal. Please explain the
technical reason for this practice.
Answer / k.prakashchandra
This is done while meggering ,so that the measured value
will not be less, due to the proximity of cable with the body.
| Is This Answer Correct ? | 3 Yes | 0 No |
To avoid arcing what we connect in earthing.
How to calculat size of copper & aluminium ?
How shall i design a liquid rotor starter
what is deffrence between squirral cage and wound rotor in IM?
why put integration for capacitorand differation for inductance
What device is use for metering current at lt consumer end..??
A d.c. Shunt motor is found suitable to drive fans because they require?
sourse is 66 KV / 350 MVA, transfarmer is 1000 KVA 6.6 / 0.415 kv, iF fault is 28.75 MVA on 0.415 KV Bus then calculat the Transfarmer Impidance
how to improve power factor correction?
which of the folowing has negative temperature coefficient of resistance? a. mercury b. copper c. lead d. carbon
What is the drawback of class b amplifier? How is this minimized?
How does frequency affect KVA rating of a transformer? If a 500 kva, 500 to 250 v, 60 hz t/f normally used in Canada is to be operated in Europe on 50 hz frequency then how will its KVA rating change? a-increase b-decrease c-remains same
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)