Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Hai I have 2500KVA,Transformer,13.8KV/380.DELTA/STAR.How
much load that I can take interms of current?How can I
calculate also when I have loads in KW?

Answers were Sorted based on User's Feedback



Hai I have 2500KVA,Transformer,13.8KV/380.DELTA/STAR.How much load that I can take interms of curr..

Answer / shalini.b

Transformer Ratio is given by
k=(v1/v2)=(N1/N2)=(i2/i1)
where
V1 : voltage at the primary side
V2 : Voltage at secondary side
like wise for current(i)& Number of turns(N)

k= V1 /V2
= 13800/380
=36.31

P=1.73*V*i*cos(phi)

input power
p1=1.73*v1*i1*cos(phi)
i1=(2500*0.8)/ (1.73*13.8*0.8)
= 104 Amps

k = i2 /i1
So i2 = 104*36.31
=3776

Is This Answer Correct ?    15 Yes 6 No

Hai I have 2500KVA,Transformer,13.8KV/380.DELTA/STAR.How much load that I can take interms of curr..

Answer / k.murugesan - tamil nadu

In Delta Connection

Line Voltage VL = Phase Voltage VP But Line Current IL =
1.73205 times of Phase Current IP.

In Star Connection

Line Voltage VL = 1.73205 times of Phase Voltage VP But Line
Current IL = Phase Current IP.

Is This Answer Correct ?    4 Yes 1 No

Hai I have 2500KVA,Transformer,13.8KV/380.DELTA/STAR.How much load that I can take interms of curr..

Answer / harpreet

primary current- 104.61A
secondry current- 3798.52A
KW- 2000

Is This Answer Correct ?    2 Yes 1 No

Hai I have 2500KVA,Transformer,13.8KV/380.DELTA/STAR.How much load that I can take interms of curr..

Answer / k.murugesan

Hi I am K.Murugesan BE EEE working at Tidel Park Ltd Chennai
as a O&M Manager.
KVA=1.732*V*I
KW=1.732*V*I*Cos.Phi

Primary Current=KVA/(1.732*13.8KV)
Primary Current= 2500/(1.732*13.8)
= 104.592A(HT.Amps)

Load Current/Secondary Current = 2500/(1.732*380)
Load Current/Secondary Current = 3.798357 KA
= 3798.357A (LT Amps)
You can Load up to 80% of Loads with safe operation.

Transformer does not consider PF.
It is only on Load side have to be maintain 0.8Lag to Unity.

Regards
K.Murugesan.
9789048244

Is This Answer Correct ?    2 Yes 2 No

Hai I have 2500KVA,Transformer,13.8KV/380.DELTA/STAR.How much load that I can take interms of curr..

Answer / musaad al-mutairi

hello ,
i want to ask about the connection because no body talked
about the role of delt/star connection
do you have any useful point
thanks all

Is This Answer Correct ?    1 Yes 2 No

Hai I have 2500KVA,Transformer,13.8KV/380.DELTA/STAR.How much load that I can take interms of curr..

Answer / tapan

Total power in kw =2000 kw
primary current of trafo is
181 amp (roundfigure)
secondary current is 6578
amp

Is This Answer Correct ?    0 Yes 1 No

Hai I have 2500KVA,Transformer,13.8KV/380.DELTA/STAR.How much load that I can take interms of curr..

Answer / saqib haroon

as per my point of view,answer of the input current is
wrong. Why the respectable brother put power factore value
with KVA rating, as per formula only once we will put PF
value, which will divide this KVA rating.

In this case the answer will be
P1= 1.73*V1*I1*cosphi
2500= 1.73*13.8*I1*0.8
2500/1.73*13.8*0.8= I1
131 A = I1

Remaining portion is OK

Is This Answer Correct ?    3 Yes 5 No

Hai I have 2500KVA,Transformer,13.8KV/380.DELTA/STAR.How much load that I can take interms of curr..

Answer / sanjay kolambekar

3798 A at unity power faactor and it can very linerly with
change in P.F

Is This Answer Correct ?    0 Yes 3 No

Hai I have 2500KVA,Transformer,13.8KV/380.DELTA/STAR.How much load that I can take interms of curr..

Answer / satheesh kumar

Primary Current is 181.15 Amps.
Secondary Current is 6578.65 Amps.
Power is 3463.8 KW

Is This Answer Correct ?    4 Yes 13 No

Hai I have 2500KVA,Transformer,13.8KV/380.DELTA/STAR.How much load that I can take interms of curr..

Answer / piyush rana

Are Karani,
I think you are not electrical engineer, it is a basic
thing,
You just calculate through following formulas :
KW= 1.732 * V * I * Cosphi

KVA=1.732 * V * I
So, I= 1.732*1000/(V * I)

Is This Answer Correct ?    1 Yes 15 No

Post New Answer

More Electrical Engineering Interview Questions

1.what is difference in maintain Hz again Hz in USA ? 2.how to calculate the battery AH? 3.why are yearly maintained in transformer how many tests in required?

0 Answers   Areva, Google,


What is the major difference between P.T. & C.V.T ? Why CVT is used in HT Transmission line in place of P.T.?

13 Answers   APGenco, OPTCL,


.if the vector group of two transformers is not same n tey r connected in parallel operation then what will happen?

2 Answers   ABB,


Which oil can be used in transformer?

1 Answers  


hi frienda We have 250kva cater pillet dg set we are fasing one diffrent proublam in dg we are start dg set after one mint applying load around 450a load but dg was run 3 Or 4 mints after 3 mints dg was shuding down automatic how to face this proublam pls tel any budy

2 Answers  


TO operate transformers in parallel, vector symbol of the both should be same.If one transformer name plate is not there, how can we conclude that whether the transformer is having the same vector symbol or not?

4 Answers  


Is electro plating what type of load whether resistive, inductive or capacitive loads

0 Answers   Apollo,


how can decide the current rating of oltc

0 Answers  


What is the relation of current with torque when motor started in Y-connection???

4 Answers  


KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these transformer has big size? Give reason

4 Answers   Suzlon,


In single phase ac ups supply when current is measured with tong tester neutral current is found more than phase current.What is the reason?

0 Answers  


Please tell me the earthing procedures adopted for the STAR-STAR 3 Phase transformer in india and give a better sugession for earthing

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)