Hai I have 2500KVA,Transformer,13.8KV/380.DELTA/STAR.How
much load that I can take interms of current?How can I
calculate also when I have loads in KW?
Answers were Sorted based on User's Feedback
Answer / shalini.b
Transformer Ratio is given by
k=(v1/v2)=(N1/N2)=(i2/i1)
where
V1 : voltage at the primary side
V2 : Voltage at secondary side
like wise for current(i)& Number of turns(N)
k= V1 /V2
= 13800/380
=36.31
P=1.73*V*i*cos(phi)
input power
p1=1.73*v1*i1*cos(phi)
i1=(2500*0.8)/ (1.73*13.8*0.8)
= 104 Amps
k = i2 /i1
So i2 = 104*36.31
=3776
| Is This Answer Correct ? | 15 Yes | 6 No |
Answer / k.murugesan - tamil nadu
In Delta Connection
Line Voltage VL = Phase Voltage VP But Line Current IL =
1.73205 times of Phase Current IP.
In Star Connection
Line Voltage VL = 1.73205 times of Phase Voltage VP But Line
Current IL = Phase Current IP.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / harpreet
primary current- 104.61A
secondry current- 3798.52A
KW- 2000
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / k.murugesan
Hi I am K.Murugesan BE EEE working at Tidel Park Ltd Chennai
as a O&M Manager.
KVA=1.732*V*I
KW=1.732*V*I*Cos.Phi
Primary Current=KVA/(1.732*13.8KV)
Primary Current= 2500/(1.732*13.8)
= 104.592A(HT.Amps)
Load Current/Secondary Current = 2500/(1.732*380)
Load Current/Secondary Current = 3.798357 KA
= 3798.357A (LT Amps)
You can Load up to 80% of Loads with safe operation.
Transformer does not consider PF.
It is only on Load side have to be maintain 0.8Lag to Unity.
Regards
K.Murugesan.
9789048244
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / musaad al-mutairi
hello ,
i want to ask about the connection because no body talked
about the role of delt/star connection
do you have any useful point
thanks all
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / tapan
Total power in kw =2000 kw
primary current of trafo is
181 amp (roundfigure)
secondary current is 6578
amp
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / saqib haroon
as per my point of view,answer of the input current is
wrong. Why the respectable brother put power factore value
with KVA rating, as per formula only once we will put PF
value, which will divide this KVA rating.
In this case the answer will be
P1= 1.73*V1*I1*cosphi
2500= 1.73*13.8*I1*0.8
2500/1.73*13.8*0.8= I1
131 A = I1
Remaining portion is OK
| Is This Answer Correct ? | 3 Yes | 5 No |
Answer / sanjay kolambekar
3798 A at unity power faactor and it can very linerly with
change in P.F
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / satheesh kumar
Primary Current is 181.15 Amps.
Secondary Current is 6578.65 Amps.
Power is 3463.8 KW
| Is This Answer Correct ? | 4 Yes | 13 No |
Are Karani,
I think you are not electrical engineer, it is a basic
thing,
You just calculate through following formulas :
KW= 1.732 * V * I * Cosphi
KVA=1.732 * V * I
So, I= 1.732*1000/(V * I)
| Is This Answer Correct ? | 1 Yes | 15 No |
1.what is difference in maintain Hz again Hz in USA ? 2.how to calculate the battery AH? 3.why are yearly maintained in transformer how many tests in required?
What is the major difference between P.T. & C.V.T ? Why CVT is used in HT Transmission line in place of P.T.?
.if the vector group of two transformers is not same n tey r connected in parallel operation then what will happen?
Which oil can be used in transformer?
hi frienda We have 250kva cater pillet dg set we are fasing one diffrent proublam in dg we are start dg set after one mint applying load around 450a load but dg was run 3 Or 4 mints after 3 mints dg was shuding down automatic how to face this proublam pls tel any budy
TO operate transformers in parallel, vector symbol of the both should be same.If one transformer name plate is not there, how can we conclude that whether the transformer is having the same vector symbol or not?
Is electro plating what type of load whether resistive, inductive or capacitive loads
how can decide the current rating of oltc
What is the relation of current with torque when motor started in Y-connection???
KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these transformer has big size? Give reason
In single phase ac ups supply when current is measured with tong tester neutral current is found more than phase current.What is the reason?
Please tell me the earthing procedures adopted for the STAR-STAR 3 Phase transformer in india and give a better sugession for earthing
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)