IF we have 500kva transformer & know the current on HT & LT side, how can we consider for its breaker?
Answers were Sorted based on User's Feedback
breaker rating is selected near to the calculated current of equipment and standard rating of breakers. but it is very important to know the fault current of that
system/ckt where it to be attached.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / kshirod
all are wrong
am telling you a simple method
always follow the thumb rule which is 500kva*1.39=695amp
bt every transformer can take extra 10% amp load
so you can use 800 amp mdo typae 3 pole l&t make acb in the
lt side
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / maze one
S = I x V x sq. root of 3
where:
S = Apparent Power, VA
I = Current, A
V = Voltage, V
note : use sq. root of 3 if the system is 3 phase
let's say Voltage = 460V @ Secondary Side
I = (500,000 VA)/(460V)(sq. root of 3)
I = 1,882.66 A
you may multiply the safety factor by 125% to 250%
or using inversed time circuit breaker by 250%
I will use 125% only, that is safe
I = 1882.66 x 125%
I = 2,353.325 AT
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / roy
ROUT 3*V*I=KVA
SO FIRST YOU SHOULD MENTION THE VOLTAGE.
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / jords
for single phase- 500,000 divided by the voltage times 80% for
your safety factor equals your C.B. size.
for three phase- 500,000 divided by the voltage divided by
square root of three times 80% for your
safety factor equals C.B. size.
Is This Answer Correct ? | 0 Yes | 2 No |
what is power factor ? why is it so important?
what are the ratings of sockets?
What are the safety equipments you should use while you are in a hvac switch yard
1 Answers GPSC Gujarat Public Service Commission,
800A 22KV TP OCB. explain
which pump used in WTP explain the function of VFD how to dtermine capacitorbank of capacity one plant
we all know voltage is a force(emf), and the force always devides if 2 or more than2 loads are there but why does the voltage remains same is parallel, it must devide na ???
WHAT IS SERVO MOTOR
why stator winding of synchronous machine are connected in star connection ?
what is meant by dielectirc medium? what is the dielectirc value of air and water???
how many types of ratings are there of transformer
for 1000kva transformer how kvar rating is need for this PFI plant. and how does it will calculate? and Apmpere rating of main cable connection?
6 Answers Engineers India, GCC, KP, QPSL, Siemens,
( Re: WHAT SHOULD BE THE RATING OF MCCB FOR 415V,3Ph,50KVAR CAPACITOR BANK Answer # 1 The capacitor current would be kvar x 1000 / (415 x sqrt3). This would be 70a approx. The MCCB selected should have *atleast 1.4 times this current i.e. 1.4 x 70= 98. So you should choose at least 100 A mccb.) regarding to this answer,i would like to know why the current have to times 1.4 to get the right amphere for the mccb.hows the formula to get the 1.4??tq