How to calculate the current rating of power cables ?
You need to know the distace between source of supply and
the load. consider a voltagedrop of 5%. i.e. 5V for a 440v
system. use the formula V=IR from this you will know the
resistance required for your requirement. (I is the load
that you want to connect). Use R=Pl/a to find the correct
cross section of the cable. (P is resistivity of either
copper or Aluminium, l is the distance).
| Is This Answer Correct ? | 12 Yes | 7 No |
for which possible reasons a motor can fail to start??
How the starter control the starting current in three phase AC Motor?(In DC apply the reistance).
what is inrush curent.
why is a avtomatic voltage regulator used for?
How do you change an AC motor to DC? why there is only 50 Hz frequency in india & not other?
how the speed decreases of a generator in power station if load increases
whenewher three phase supply is given to induction motors revolving/rotating field is created & rotor rotates.When the three phase supply is given to three phase transformer then revolving,/rotating field is created or not? if not why?
Where can I get Iidian straderd specifications for electrical items or works in web? please help me.
Wht is the meaning of floating neutral
why we choose 50 or 60 hertz not other value for the power system?
What is the meaning of utility ground and clean ground? How the distribution panel is grounded?
why high speed tripping relay will be used in tripping circuit why not normal relay
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)