Generally in AC we consider voltage, frequency and phase
sequence for parallel operation ... Can we parallel two DC
battery chargers? If yes, then what precaution to be taken
when we parallel two DC power?
Answers were Sorted based on User's Feedback
Answer / vijaykumar shetye
1) Yes, theoretically, we can parallel two DC battery
chargers, but generally they are not designed for parallel
operation.
2) Following factors are to be considered.
1) The voltage of both the chargers should be the same.
2) Both chargers should be connected in the same
polarity.
3) The output impedance of both the chargers should be
the same, so that both deliver equal current. (It is not
necessary that both the chargers should be of the same
make. It would rather prefer same model than same make.)
4) The characteristics of both the chargers should be the
same. Both should be set at the same current setting for
changeover from boost to float.
5) The current capacity of both the chargers should be
the same.
Is This Answer Correct ? | 12 Yes | 0 No |
Answer / pankaj verma
Main criteria for parallel connection is :
1. Both chargers should be connected in the same polarity.
2. Voltage of both the chargers should be same.
3. chargers should have identical specification.
Practically chargers are never used in parallel, they are
just momentarily paralleled in order to shift load of each
other so that maintenance work on each one can be carried out.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / omkar
) The voltage of both the chargers should be the same.
2) Both chargers should be connected in the same
polarity.
3) The output impedance of both the chargers should be
the same, so that both deliver equal current. (It is not
necessary that both the chargers should be of the same
make. It would rather prefer same model than same make.)
4) The characteristics of both the chargers should be the
same. Both should be set at the same current setting for
changeover from boost to float.
5) The current capacity of both the chargers should be
the same.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vinod
DC battery charger is feeding the float& DC load curent,
when AC fails battery will feed the DC,if charger fails
another charger can put in service.DC battery chargers not
required to parallel.(ie. battery having C10 capacity 100
AH or more)
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ramprasad
Before parallel operation of two DC Battery charger
precaution to be taken is
1. Both Battery charger must to be same make.
2. Output of Battery charger output must to same volt.
3. Primary of both charger must to be connected in parallel
with same phase sequence.
4. Output of Charger connected in parallel with same
polarity.
5. Voltage regulation must be very perfect of charger.
Is This Answer Correct ? | 5 Yes | 8 No |
What causal system?
What are protections for dty type transformers
after how many spot we must chang secondry cable in portable spot welding gun?
Dear sir, my knowledge about cable size determination is limited. Though I read examples I could not calculate the Cable size required for electric driven pump 40 KW, 380 Volt, 50 HZ, 50 meter from transformer and it is three phase star delta starting. Please help as there is no one in my surroundings to help.
What is SF6 Circuit Breaker?
In a 3 phase system a neutral exists so that any unbalanced currents can flow through it towards earth.... but a phase demands a particular current as per the load attached to it....then where does the extra current come from the goes in the neutral??....I mean in an unbalanced system a phase demands a current as per its load attached....then where does the unbalanced current come from??
why stone used in Transformer yard.
HOW CAN YOU CALCULATE PRACTICAL EFFICIENCY OF A ASYNCHRONOUS INDUCTIONMOTOR OF 7.5KW,& MOTOR IS RUNNING WITH AVOLTAGE OF 410 VOLTS,& TAKING CURENT OF 13 AMPS
In UPS, battery connections if parallel connection given, what will happen?
in india ac frequency is 50hz, but in foreign countries it is 60hz,whwt is the reason
In DC current-excitation to transformer, why it sucks more current? Eventhough there is no power transfer between primary and secondary? R is very low so it should suck less current only na thn y its current increases?
What is meant by derating factor?