Answer / vijaykumar shetye
1) Yes, theoretically, we can parallel two DC battery
chargers, but generally they are not designed for parallel
operation.
2) Following factors are to be considered.
1) The voltage of both the chargers should be the same.
2) Both chargers should be connected in the same
polarity.
3) The output impedance of both the chargers should be
the same, so that both deliver equal current. (It is not
necessary that both the chargers should be of the same
make. It would rather prefer same model than same make.)
4) The characteristics of both the chargers should be the
same. Both should be set at the same current setting for
changeover from boost to float.
5) The current capacity of both the chargers should be
the same.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / pankaj verma
Main criteria for parallel connection is :
1. Both chargers should be connected in the same polarity.
2. Voltage of both the chargers should be same.
3. chargers should have identical specification.
Practically chargers are never used in parallel, they are
just momentarily paralleled in order to shift load of each
other so that maintenance work on each one can be carried out.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / omkar
) The voltage of both the chargers should be the same.
2) Both chargers should be connected in the same
polarity.
3) The output impedance of both the chargers should be
the same, so that both deliver equal current. (It is not
necessary that both the chargers should be of the same
make. It would rather prefer same model than same make.)
4) The characteristics of both the chargers should be the
same. Both should be set at the same current setting for
changeover from boost to float.
5) The current capacity of both the chargers should be
the same.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vinod
DC battery charger is feeding the float& DC load curent,
when AC fails battery will feed the DC,if charger fails
another charger can put in service.DC battery chargers not
required to parallel.(ie. battery having C10 capacity 100
AH or more)
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ramprasad
Before parallel operation of two DC Battery charger
precaution to be taken is
1. Both Battery charger must to be same make.
2. Output of Battery charger output must to same volt.
3. Primary of both charger must to be connected in parallel
with same phase sequence.
4. Output of Charger connected in parallel with same
polarity.
5. Voltage regulation must be very perfect of charger.
| Is This Answer Correct ? | 5 Yes | 8 No |
what is derating?, why it is neccesary, it is same for all means for drives, motors,and cables.
what is the use of capacitor in online ups?
in soft starter system for 375 KW 3 ph induction motor for multi stage vertical pump, two thyristers failed causing shorting of thyrister. the motor winding failed while starting.What is the cause and what is the effect in above case
what is the funda of earthing? Explain breifly about earthing?
What are the criteria shall be considers for sizing Fuse and MCB? If the rated current is 10Amps what should be the fuse size / MCB Size?
How to calcualte 1unit of current consumption?
3 Answers Bhushan Power Steel, ITC Infotech,
what is difference between earhing and neutral
why power factor is lagging and leading(i.e -1to +1)
After synchronization with grid what is the demand value QKVAR and how we will maintain that?
What is the magnetic field (coil DC ) of Turbo Expander?
Why a single-phase induction motor not an inherently self-starting machine?
11 Answers ETC, Hindustan Shipyard,
why efficiency of generator is greater than motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)