Answer / tabaraz
starter is used to synchronise the starting current with the requred limit.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sonu rajput
1) Rotar current is depend upon
1.stator voltage (V1)
2.Leakage reactance of rotar (X2)
2) If ratated voltage is applied to motor ,motor draws heavy current at starting.
3) Hence, to reduce the heavy starting current at the starting of IM starters are used.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sudhir
T=FLUX*I*POWER FACTOR, as time of starting s=1
so reactance is very large in comperision to
resistance(normaly is very low) for constant load(and
inertia) the power factor(theta=reactance/resistance is
large) is very less(flux is constant) so starting current
is very large so Starter is used to reduce starting current.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / r.siddharth
At the instant of starting, the rotor is stationary, thus
slip being unity, the frequency of the rotor emf equals the
supply frequency and the rotor emf induced per phase is
quite large.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / p k neeraj
at the time of starting of induction motor speed is zero,so
back emf is also zero,as back emf is zero & rotor coil is
sorted(in case of squirrel cage rotor),starting current is
about 5 to 6 times higher then the rated current.so because
of this high voltage drop gets created in the supply line &
equipment connected to this line will experience this.so to
reduce the high current generally we use star delta
starter.at the time of starting we use star connection so
the voltage got reduce then at the time of run we use delta
connection.......
starters also increase the starting torque & improves the
power factor.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / kkkk
starter is for help to when over-voltage coming it will help the motor from destruction
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / arun mutharasu
consider a equation ( kvl form in starting period )
V=Eb+IR
at starting time,
the back emf is zero,
so I=V/R,
In case the R is small mean,
eg) v=220 Volt, R=.5 Ohm sub this and get I=440 Amps,
that reason we increase the starting resistance of the
motor using starter.
| Is This Answer Correct ? | 1 Yes | 7 No |
can u please mail me the syllabus for GET exam for damodar valley corporation?
how rated the neutral voltage of transformer and reactor, e.g. 400/220, 200MVA transformer have neutral voltage of 33kv. and reactor voltage 145kv. how this rating decided?
What you have to see in transformer after week, month?
What is boucholz relay and the significance of it in to the trformer?
why dc is not given to transformer
What is the differance between negative dc voltage and positive dc voltage because some circuit uses -24,-5,-12,- 15,volt dc supply
10 Answers eLab, Hero Honda, NTPC, Suzlon, Teradyne,
1.25 kg of hydrogen are burnt with stiochiometric air, the mass of air in kg required is
time constant of RC series circuit?
Why a motor blower cobination draw more current at winter than summer?
what is the relation between currebt & voltage.
How to do cable sizing calculation for 750 A Neutral Earthing resistor for 33kv. the 33kv cable going to swbd. is 630mm2 3 runs.
state application of relay in transmission line?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)